LM as Modbus Slave. datatype and offset
Hi! I ask for your help, I am a beginner.
I am using LM as Slave via script.
When I try to write an integer value in my PLC to an integer register (uint16 in LM), I cannot do it. But if I write a floating point value to this register, then an integer value is written.
When I test in Modbus Poll, I have the status “illegal data address” Slave LM.
is it an offset problem? What should I do?
It might help if you show us the slave script.
if not mb then   require('genohm-scada.eibdgm')   require('luamodbus')   -- list of coil mapping, starting from 0   coils = { '1/1/1', '1/1/2','1/1/3' ,'1/1/4' }   -- list of register mapping, starting from 0   registers = { '3/1/1', '3/1/2'}   -- list of register data types, element count must match registers table   regdt = { dt.uint16,dt.uint16}   -- knx group write callback   function knxgroupwrite(event)     local value     -- try to find matching coil     for id, addr in ipairs(coils) do       if event.dst == addr then         value = knxdatatype.decode(event.datahex, dt.bool)         mb:setcoils(id - 1, value)               end     end     -- try to find matching register     for id, addr in ipairs(registers) do       if event.dst == addr then         value = knxdatatype.decode(event.datahex, regdt[ id ])         mb:setregisters(id - 1, value)               end     end   end   -- coil write callback   function mbwritecoils(coil, value)     local addr = coils[ coil + 1 ]     if addr then       grp.write(addr, value, dt.bool)     end   end   -- register write callback   function mbwriteregisters(register, value)     local addr = registers[ register + 1 ]     if addr then       grp.write(addr, value, regdt[ register + 1])     end   end   -- knx group monitor, handles group writes   knxclient = eibdgm:new({ timeout = 0.1 })   knxclient:sethandler('groupwrite', knxgroupwrite)   -- modbus slave, listen on all interfaces and default port 502   mb = luamodbus.tcp()   mb:open('хх.хх.хх.хх', 502)   -- setting slave id is optional   --mb:setslave(1)   mb:setreceivetimeout(0.1)   mb:setmapping(#coils, 0, #registers, 0)   -- init coils   for id, addr in ipairs(coils) do     value = grp.getvalue(addr)     mb:setcoils(id - 1, value)   end   -- init registers   for id, addr in ipairs(registers) do     value = grp.getvalue(addr)     mb:setregisters(id - 1, value)   end   -- set callbacks for coil and register write   mb:setwritecoilcb(mbwritecoils)   mb:setwriteregistercb(mbwriteregisters) end -- handle modbus and knx mb:handleslave() knxclient:step()
changed nothing Sad
You have done everything correct here. I assume the objects 3/1/1 and 3/1/2 are 2 byte unsigned integer?
Which address are you using from ModBus side? You can only use 0 and 1 because you have 2 registers defined.
(27.11.2020, 10:11)admin Wrote: Which address are you using from ModBus side? You can only use 0 and 1 because you have 2 registers defined.
yes. use 0 and 1 registers
immediately after connecting to LM
and I can write data from Modbus Poll. But from one type PCL i can not. and from other type PLC I can only when I write float
(27.11.2020, 10:09)Daniel. Wrote: You have done everything correct here. I assume the objects 3/1/1 and 3/1/2 are 2 byte unsigned integer?
yes
I think maybe my controller starts reading not from 0, but from 16 bits. therefore, he understands part of the float as integer. And i need to do offset. is it possible?
please, can you test this script in some Modbus Server? do you get an "illegal data address" too?
"illegal data address" : The data address received in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid.
This script was used in many projects and nobody had this issue. Try reading register 1.
yes-yes! i totally agree with you. i see how many people use it. i only want to understand where is my issues. i can read and write values via modbus server but with errors.
The issue is somewhere in config of your PLC.
PS. LM is modbus server here, your PLC is client.
(27.11.2020, 13:22)Daniel. Wrote: The issue is somewhere in config of your PLC.
yes! it was PLC issues. Thank you for the help!