This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM as Modbus Slave. datatype and offset
#1
Hi! I ask for your help, I am a beginner.
I am using LM as Slave via script.

When I try to write an integer value in my PLC to an integer register (uint16 in LM), I cannot do it. But if I write a floating point value to this register, then an integer value is written.
When I test in Modbus Poll, I have the status “illegal data address” Slave LM.

is it an offset problem? What should I do?
Reply
#2
It might help if you show us the slave script.
------------------------------
Ctrl+F5
Reply
#3
Code:
if not mb then
  require('genohm-scada.eibdgm')
  require('luamodbus')

  -- list of coil mapping, starting from 0
  coils = { '1/1/1', '1/1/2','1/1/3' ,'1/1/4' }

  -- list of register mapping, starting from 0
  registers = { '3/1/1', '3/1/2'}

  -- list of register data types, element count must match registers table
  regdt = { dt.uint16,dt.uint16}

  -- knx group write callback
  function knxgroupwrite(event)
    local value

    -- try to find matching coil
    for id, addr in ipairs(coils) do
      if event.dst == addr then
        value = knxdatatype.decode(event.datahex, dt.bool)
        mb:setcoils(id - 1, value)
       
      end
    end

    -- try to find matching register
    for id, addr in ipairs(registers) do
      if event.dst == addr then
        value = knxdatatype.decode(event.datahex, regdt[ id ])
        mb:setregisters(id - 1, value)
       
      end
    end
  end

  -- coil write callback
  function mbwritecoils(coil, value)
    local addr = coils[ coil + 1 ]
    if addr then
      grp.write(addr, value, dt.bool)
    end
  end

  -- register write callback
  function mbwriteregisters(register, value)
    local addr = registers[ register + 1 ]
    if addr then
      grp.write(addr, value, regdt[ register + 1])
    end
  end

  -- knx group monitor, handles group writes
  knxclient = eibdgm:new({ timeout = 0.1 })
  knxclient:sethandler('groupwrite', knxgroupwrite)

  -- modbus slave, listen on all interfaces and default port 502
  mb = luamodbus.tcp()
  mb:open('хх.хх.хх.хх', 502)

  -- setting slave id is optional
  --mb:setslave(1)

  mb:setreceivetimeout(0.1)
  mb:setmapping(#coils, 0, #registers, 0)

  -- init coils
  for id, addr in ipairs(coils) do
    value = grp.getvalue(addr)
    mb:setcoils(id - 1, value)
  end

  -- init registers
  for id, addr in ipairs(registers) do
    value = grp.getvalue(addr)
    mb:setregisters(id - 1, value)
  end

  -- set callbacks for coil and register write
  mb:setwritecoilcb(mbwritecoils)
  mb:setwriteregistercb(mbwriteregisters)
end

-- handle modbus and knx
mb:handleslave()
knxclient:step()

changed nothing Sad
Reply
#4
You have done everything correct here. I assume the objects 3/1/1 and 3/1/2 are 2 byte unsigned integer?
------------------------------
Ctrl+F5
Reply
#5
Which address are you using from ModBus side? You can only use 0 and 1 because you have 2 registers defined.
Reply
#6
(27.11.2020, 10:11)admin Wrote: Which address are you using from ModBus side? You can only use 0 and 1 because you have 2 registers defined.
yes. use 0 and 1 registers

immediately after connecting to LM

and I can write data from Modbus Poll. But from one type PCL i can not. and from other type PLC I can only when I write float

(27.11.2020, 10:09)Daniel. Wrote: You have done everything correct here. I assume the objects 3/1/1 and 3/1/2 are 2 byte unsigned integer?
yes

I think maybe my controller starts reading not from 0, but from 16 bits. therefore, he understands part of the float as integer. And i need to do offset. is it possible?
Reply
#7
please, can you test this script in some Modbus Server? do you get an "illegal data address" too?

"illegal data address" : The data address received in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid.
Reply
#8
This script was used in many projects and nobody had this issue. Try reading register 1.
------------------------------
Ctrl+F5
Reply
#9
yes-yes! i totally agree with you. i see how many people use it. i only want to understand where is my issues. i can read and write values via modbus server but with errors.
Reply
#10
The issue is somewhere in config of your PLC.
PS. LM is modbus server here, your PLC is client.
------------------------------
Ctrl+F5
Reply
#11
(27.11.2020, 13:22)Daniel. Wrote: The issue is somewhere in config of your PLC.
PS. LM is modbus server here, your PLC is client.
yes! it was PLC issues. Thank you for the help!