This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus Error Log
#1
Hello
I have errors in the Modbus error Logs but the slave devices are working, I can read and write.
errors are: 
- read failed: operation timed out
- read failed: response not from requested slave
I got a lot of these errors in the error log

is it ok to see these errors? 

Note that I have slave devices on Modbus TCP with no errors
Best Regards,
Reply
#2
It means that there are some minor issues with the RS485 communication.
Some things to consider:
1. Connect GND between all Modbus devices (read this: https://store.chipkin.com/articles/rs485...wire-rs485)
2. Install 120 ohm terminator resistor on both ends of the RS485 bus
3. Topology: daisy-chain connection is recommended. Short stubs are OK as well, never use star topology
4. Try using a lower baud rate if devices allow this
Reply
#3
(19.04.2021, 06:25)admin Wrote: It means that there are some minor issues with the RS485 communication.
Some things to consider:
1. Connect GND between all Modbus devices (read this: https://store.chipkin.com/articles/rs485...wire-rs485)
2. Install 120 ohm terminator resistor on both ends of the RS485 bus
3. Topology: daisy-chain connection is recommended. Short stubs are OK as well, never use star topology
4. Try using a lower baud rate if devices allow this

Thank You, Admin