ocpp and knx homelynk
I have a charge point  that works with ocpp. I wanna connect it to my homelynk and operated with knx but i don't know how to connect it .
Any idea?
Do you have a SE charger? If yes you could use Modbus IP in the scenario.. I haven't seen any direct implementation of the open charge point protocol until now but with our chargers we use Modbus for local status and control and use OCPP only to connect the device to a public enabled platform.
Hello Erwin,
I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible?
Thank you for your help
(11.10.2021, 22:52)Erwin van der Zwart Wrote: Do you have a SE charger? If yes you could use Modbus IP in the scenario.. I haven't seen any direct implementation of the open charge point protocol until now but with our chargers we use Modbus for local status and control and use OCPP only to connect the device to a public enabled platform.
No, I cant use Modbus, that's my problem.
(12.10.2021, 07:38)Kilogica Wrote: Hello Erwin,
Yes it should have modbus as i already integrated this one on a project.. I disabled the not needed registers but kept them in the script
12345678910111213141516171819202122232425262728293031323334353637383940414243444546474849
require('luamodbus') mb = luamodbus.tcp() -- Read Socket 1 mb:open('192.168.1.200', 502) mb:connect() mb:setslave(255) --s1AL1 = mb:readregistervalue(350, 'float32', 'w') -- Current Phase 1 --s1AL2 = mb:readregistervalue(352, 'float32', 'w') --s1AL3 = mb:readregistervalue(354, 'float32', 'w') s1ET = mb:readregistervalue(356, 'uint32', 'w') -- Energy Total --s1PT = mb:readregistervalue(358, 'float32', 'w') -- Current Power --s1VL1L2 = mb:readregistervalue(360, 'float32', 'w') -- Voltage Phase 1 - Phase 2 --s1VL2L3 = mb:readregistervalue(362, 'float32', 'w') --s1VL3L1 = mb:readregistervalue(364, 'float32', 'w') --s1VL1N = mb:readregistervalue(366, 'float32', 'w') -- Voltage Phase 1 - Neutral --s1VL2N = mb:readregistervalue(368, 'float32', 'w') --s1VL3N = mb:readregistervalue(370, 'float32', 'w') --log(s1AL1,s1AL2,s1AL3,s1ET,s1PT,s1VL1L2,s1VL2L3,s1VL3L1,s1VL1N,s1VL2N,s1VlLN) mb:close() -- Read Socket 2 mb:open('192.168.1.201', 502) mb:connect() mb:setslave(255) --s2AL1 = mb:readregistervalue(350, 'float32', 'w') --s2AL2 = mb:readregistervalue(352, 'float32', 'w') --s2AL3 = mb:readregistervalue(354, 'float32', 'w') s2ET = mb:readregistervalue(356, 'uint32', 'w') --s2PT = mb:readregistervalue(358, 'float32', 'w') --s2VL1L2 = mb:readregistervalue(360, 'float32', 'w') --s2VL2L3 = mb:readregistervalue(362, 'float32', 'w') --s2VL3L1 = mb:readregistervalue(364, 'float32', 'w') --s2VL1N = mb:readregistervalue(366, 'float32', 'w') --s2VL2N = mb:readregistervalue(368, 'float32', 'w') --s2VL3N = mb:readregistervalue(370, 'float32', 'w') --log(s2AL1,s2AL2,s2AL3,s2ET,s2PT,s2VL1L2,s2VL2L3,s2VL3L1,s2VL1N,s2VL2N,s2VL3N) mb:close() -- Sum Socket 1 and Socket 2 tET = s1ET + s2ET -- Sum energy total of socket 1 and 2 tETrounded = math.round(tET/1000,0) -- Total S + S2 from Wh to kWh s1ET = math.round(s1ET/1000,0) -- Socket 1 from Wh to kWh s2ET = math.round(s2ET/1000,0) -- Socket 2 from Wh to kWh grp.checkupdate('4/1/22', s1ET) -- Update values grp.checkupdate('4/1/23', s2ET) grp.checkupdate('4/1/19', tETrounded)
Thank you! It Works!
I looked everywhere but I can't find anything in the documentation