		I have a charge point  that works with ocpp. I wanna connect it to my homelynk and operated with knx but i don't know how to connect it . 
Any idea?
	 
	
	
	
		
	 
 
 
	
	
	
		
	Posts: 1807 
	Threads: 7 
	Joined: Jul 2015
	
 Reputation: 
 121
	 
 
	
	
		Do you have a SE charger? If yes you could use Modbus IP in the scenario.. I haven't seen any direct implementation of the open charge point protocol until now but with our chargers we use Modbus for local status and control and use OCPP only to connect the device to a public enabled platform.
	 
	
	
	
		
	 
 
 
	
	
	
		
	Posts: 94 
	Threads: 29 
	Joined: Nov 2020
	
 Reputation: 
 1
	 
 
	
	
		Hello Erwin, 
 
I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible? 
 
Thank you for your help
	 
	
	
	
		
	 
 
 
	
	
	
		
	Posts: 4 
	Threads: 2 
	Joined: May 2021
	
 Reputation: 
 0
	 
 
	
	
		 (11.10.2021, 22:52)Erwin van der Zwart Wrote:  Do you have a SE charger? If yes you could use Modbus IP in the scenario.. I haven't seen any direct implementation of the open charge point protocol until now but with our chargers we use Modbus for local status and control and use OCPP only to connect the device to a public enabled platform. 
No, I cant use Modbus, that's my problem.
	  
	
	
	
		
	 
 
 
	
	
	
		
	Posts: 1807 
	Threads: 7 
	Joined: Jul 2015
	
 Reputation: 
 121
	 
 
	
		
		
		13.10.2021, 18:21 
(This post was last modified: 13.10.2021, 18:28 by Erwin van der Zwart.)
		
	 
	
		 (12.10.2021, 07:38)Kilogica Wrote:  Hello Erwin, 
 
I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible? 
 
Thank you for your help 
Yes it should have modbus as i already integrated this one on a project.. I disabled the not needed registers but kept them in the script
 Code: require('luamodbus') 
mb = luamodbus.tcp() 
 
-- Read Socket 1 
mb:open('192.168.1.200', 502) 
mb:connect() 
mb:setslave(255) 
--s1AL1 = mb:readregistervalue(350, 'float32', 'w') -- Current Phase 1 
--s1AL2 = mb:readregistervalue(352, 'float32', 'w') 
--s1AL3 = mb:readregistervalue(354, 'float32', 'w')  
s1ET = mb:readregistervalue(356, 'uint32', 'w') -- Energy Total 
--s1PT = mb:readregistervalue(358, 'float32', 'w') -- Current Power  
--s1VL1L2 = mb:readregistervalue(360, 'float32', 'w') -- Voltage Phase 1 - Phase 2 
--s1VL2L3 = mb:readregistervalue(362, 'float32', 'w') 
--s1VL3L1 = mb:readregistervalue(364, 'float32', 'w') 
--s1VL1N = mb:readregistervalue(366, 'float32', 'w') -- Voltage Phase 1 - Neutral 
--s1VL2N = mb:readregistervalue(368, 'float32', 'w') 
--s1VL3N = mb:readregistervalue(370, 'float32', 'w') 
--log(s1AL1,s1AL2,s1AL3,s1ET,s1PT,s1VL1L2,s1VL2L3,s1VL3L1,s1VL1N,s1VL2N,s1VlLN) 
mb:close() 
 
-- Read Socket 2 
mb:open('192.168.1.201', 502) 
mb:connect() 
mb:setslave(255) 
--s2AL1 = mb:readregistervalue(350, 'float32', 'w') 
--s2AL2 = mb:readregistervalue(352, 'float32', 'w') 
--s2AL3 = mb:readregistervalue(354, 'float32', 'w') 
s2ET = mb:readregistervalue(356, 'uint32', 'w') 
--s2PT = mb:readregistervalue(358, 'float32', 'w') 
--s2VL1L2 = mb:readregistervalue(360, 'float32', 'w') 
--s2VL2L3 = mb:readregistervalue(362, 'float32', 'w') 
--s2VL3L1 = mb:readregistervalue(364, 'float32', 'w') 
--s2VL1N = mb:readregistervalue(366, 'float32', 'w') 
--s2VL2N = mb:readregistervalue(368, 'float32', 'w') 
--s2VL3N = mb:readregistervalue(370, 'float32', 'w') 
--log(s2AL1,s2AL2,s2AL3,s2ET,s2PT,s2VL1L2,s2VL2L3,s2VL3L1,s2VL1N,s2VL2N,s2VL3N) 
mb:close() 
 
-- Sum Socket 1 and Socket 2 
tET = s1ET + s2ET -- Sum energy total of socket 1 and 2 
tETrounded = math.round(tET/1000,0) -- Total S + S2 from Wh to kWh 
 
s1ET = math.round(s1ET/1000,0) -- Socket 1 from Wh to kWh 
s2ET = math.round(s2ET/1000,0) -- Socket 2 from Wh to kWh 
 
grp.checkupdate('4/1/22', s1ET) -- Update values 
grp.checkupdate('4/1/23', s2ET)  
grp.checkupdate('4/1/19', tETrounded)
  
	 
	
	
	
		
	 
 
 
	
	
	
		
	Posts: 94 
	Threads: 29 
	Joined: Nov 2020
	
 Reputation: 
 1
	 
 
	
	
		 (13.10.2021, 18:21)Erwin van der Zwart Wrote:   (12.10.2021, 07:38)Kilogica Wrote:  Hello Erwin, 
 
I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible? 
 
Thank you for your help  
Yes it should have modbus as i already integrated this one on a project.. I disabled the not needed registers but kept them in the script 
 
Code: require('luamodbus') 
mb = luamodbus.tcp() 
 
-- Read Socket 1 
mb:open('192.168.1.200', 502) 
mb:connect() 
mb:setslave(255) 
--s1AL1 = mb:readregistervalue(350, 'float32', 'w') -- Current Phase 1 
--s1AL2 = mb:readregistervalue(352, 'float32', 'w') 
--s1AL3 = mb:readregistervalue(354, 'float32', 'w')  
s1ET = mb:readregistervalue(356, 'uint32', 'w') -- Energy Total 
--s1PT = mb:readregistervalue(358, 'float32', 'w') -- Current Power  
--s1VL1L2 = mb:readregistervalue(360, 'float32', 'w') -- Voltage Phase 1 - Phase 2 
--s1VL2L3 = mb:readregistervalue(362, 'float32', 'w') 
--s1VL3L1 = mb:readregistervalue(364, 'float32', 'w') 
--s1VL1N = mb:readregistervalue(366, 'float32', 'w') -- Voltage Phase 1 - Neutral 
--s1VL2N = mb:readregistervalue(368, 'float32', 'w') 
--s1VL3N = mb:readregistervalue(370, 'float32', 'w') 
--log(s1AL1,s1AL2,s1AL3,s1ET,s1PT,s1VL1L2,s1VL2L3,s1VL3L1,s1VL1N,s1VL2N,s1VlLN) 
mb:close() 
 
-- Read Socket 2 
mb:open('192.168.1.201', 502) 
mb:connect() 
mb:setslave(255) 
--s2AL1 = mb:readregistervalue(350, 'float32', 'w') 
--s2AL2 = mb:readregistervalue(352, 'float32', 'w') 
--s2AL3 = mb:readregistervalue(354, 'float32', 'w') 
s2ET = mb:readregistervalue(356, 'uint32', 'w') 
--s2PT = mb:readregistervalue(358, 'float32', 'w') 
--s2VL1L2 = mb:readregistervalue(360, 'float32', 'w') 
--s2VL2L3 = mb:readregistervalue(362, 'float32', 'w') 
--s2VL3L1 = mb:readregistervalue(364, 'float32', 'w') 
--s2VL1N = mb:readregistervalue(366, 'float32', 'w') 
--s2VL2N = mb:readregistervalue(368, 'float32', 'w') 
--s2VL3N = mb:readregistervalue(370, 'float32', 'w') 
--log(s2AL1,s2AL2,s2AL3,s2ET,s2PT,s2VL1L2,s2VL2L3,s2VL3L1,s2VL1N,s2VL2N,s2VL3N) 
mb:close() 
 
-- Sum Socket 1 and Socket 2 
tET = s1ET + s2ET -- Sum energy total of socket 1 and 2 
tETrounded = math.round(tET/1000,0) -- Total S + S2 from Wh to kWh 
 
s1ET = math.round(s1ET/1000,0) -- Socket 1 from Wh to kWh 
s2ET = math.round(s2ET/1000,0) -- Socket 2 from Wh to kWh 
 
grp.checkupdate('4/1/22', s1ET) -- Update values 
grp.checkupdate('4/1/23', s2ET)  
grp.checkupdate('4/1/19', tETrounded)
  
Thank you! It Works!
 
I looked everywhere but I can't find anything in the documentation
	  
	
	
	
		
	 
 
 
	 
 |