Threads: 43
05.01.2022, 09:12
(This post was last modified: 05.01.2022, 09:16 by gtsamis .)
Happy new year!
On the trends widget, if i enable the time controls they apear outside of the widget. Is there any fix for it? I would also like to modifty the displayed decimals on value widget.
Threads: 43
We will look into this. For now either disable zooming or set widget width to 3 or 5 units.
Threads: 43
I tried only the height... width worked. What about decimal places display?
Threads: 43
New update has been published. See if it fixed the issue for you. Thousands separator (",") has been removed from the trends value display. Decimals cannot be configured at this moment.
Threads: 43
(05.01.2022, 09:35) admin Wrote: We will look into this. For now either disable zooming or set widget width to 3 or 5 units.
(06.01.2022, 13:12) admin Wrote: New update has been published. See if it fixed the issue for you. Thousands separator (",") has been removed from the trends value display. Decimals cannot be configured at this moment.
Works fine, thank you.
Threads: 9
WOW,
those energy dashbords looks nice!
How do you do this in Wiser?
I have powertags, but not any daily or weekly calculations shown.
To you use the Active Energy resettable kWh an d log this some how?
GIA
Best Regards
NewBee to wiser
Threads: 6
Yes, create trends on the points you want to log and then create a visu in Touch Config, there you can add the live values and trends on a dashboard.
Threads: 9
Yeah, I`am using that function,
But how do you get the the daily summations or weekly? Are they custom widgets/tiles, with the summation done in scripting etc?
GIA
Best Regards
NewBee to wiser
Threads: 43
06.09.2022, 12:36
(This post was last modified: 06.09.2022, 12:38 by gtsamis .)
(06.09.2022, 11:51) GIA Wrote: Yeah, I`am using that function,
GIA
Intermediate counters are calculated using virtual objects and scripting...
below is a raw event script that runs on the object when it changes at least 1kw... for sure it need tunning but could help as a starting point
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253
myobjects =
grp.tag (
'CalcTotalA' )
totalA =
for _ ,
object in ipairs (
myobjects )
do
totalA =
totalA +
object.value
grp.update (
'Συνολική ένταση (A)' ,
totalA )
now =
os.date (
'*t' )
now.wday =
now.wday ==
1 and 7 or now.wday -
initTotalwh =
initT1wh =
initT2wh =
initT3wh =
initT4wh =
TotalkWh =
math.floor (
event.getvalue ()/
1000 )
T1kWh =
math.floor ((
grp.getvalue (
'Ενεργή ενέργεια Τ1 (Wh)' ) -
initT1wh ) /
1000 )
T2kWh =
math.floor ((
grp.getvalue (
'Ενεργή ενέργεια Τ2 (Wh)' ) -
initT2wh ) /
1000 )
T3kWh =
math.floor ((
grp.getvalue (
'Ενεργή ενέργεια Τ3 (Wh)' ) -
initT3wh ) /
1000 )
T4kWh =
math.floor ((
grp.getvalue (
'Ενεργή ενέργεια Τ4 (Wh)' ) -
initT4wh ) /
1000 )
grp.update (
'Συνολική ενέργεια (kWh)' ,
TotalkWh )
grp.update (
'Συνολική ενέργεια Τ1 (kWh)' ,
T1kWh )
grp.update (
'Συνολική ενέργεια Τ2 (kWh)' ,
T2kWh )
grp.update (
'Συνολική ενέργεια Τ3 (kWh)' ,
T3kWh )
grp.update (
'Συνολική ενέργεια Τ4 (kWh)' ,
T4kWh )
metinit =
storage.get (
'met:init' ,
0 )
metpt =
storage.get (
'met:pt' ,
0 )
ypt =
storage.get (
'met:year-pt' ,
0 )
ypt1 =
storage.get (
'met:year-pt1' ,
0 )
ypt2 =
storage.get (
'met:year-pt2' ,
0 )
yct =
storage.get (
'met:year-ct' ,
0 )
yct1 =
storage.get (
'met:year-ct1' ,
0 )
yct2 =
storage.get (
'met:year-ct2' ,
0 )
mpt =
storage.get (
'met:month-pt' ,
0 )
mpt1 =
storage.get (
'met:month-pt1' ,
0 )
mpt2 =
storage.get (
'met:month-pt2' ,
0 )
mct =
storage.get (
'met:month-ct' ,
0 )
mct1 =
storage.get (
'met:month-ct1' ,
0 )
mct2 =
storage.get (
'met:month-ct2' ,
0 )
daypt =
storage.get (
'met:day-pt' ,
0 )
daypt1 =
storage.get (
'met:day-pt1' ,
0 )
daypt2 =
storage.get (
'met:day-pt2' ,
0 )
dayct =
storage.get (
'met:day-ct' ,
0 )
dayct1 =
storage.get (
'met:day-ct1' ,
0 )
dayct2 =
storage.get (
'met:day-ct2' ,
0 )
wpt =
storage.get (
'met:week-pt' ,
0 )
wpt1 =
storage.get (
'met:week-pt1' ,
0 )
wpt2 =
storage.get (
'met:week-pt2' ,
0 )
wct =
storage.get (
'met:week-ct' ,
0 )
wct1 =
storage.get (
'met:week-ct1' ,
0 )
wct2 =
storage.get (
'met:week-ct2' ,
0 )
ppt =
storage.get (
'met:period-pt' ,
0 )
ppt1 =
storage.get (
'met:period-pt1' ,
0 )
ppt2 =
storage.get (
'met:period-pt2' ,
0 )
pct =
storage.get (
'met:period-ct' ,
0 )
pct1 =
storage.get (
'met:period-ct1' ,
0 )
pct2 =
storage.get (
'met:period-ct2' ,
0 )
delta =
TotalkWh-metpt
if now.month ==
1 and now.day ==
1 and now.hour ==
0 and now.min <
5 then
alert (
'Reseting Yearly, Monthly, Daily energy counters' )
grp.write (
'Επαναφορά μετρητή διακοπών ρεύματος' ,
true )
storage.set (
'met:year-pt' ,
yct +
delta )
grp.write (
'Ενέργεια προηγούμενου έτους συνολικά (kWh)' ,
yct +
delta )
storage.set (
'met:year-ct' ,
0 )
grp.write (
'Ενέργεια τρέχοντα έτους συνολικά (kWh)' ,
0 )
storage.set (
'met:year-pt1' ,
yct1 +
delta )
grp.write (
'Ενέργεια προηγούμενου έτους Τ1 (kWh)' ,
yct1 +
delta )
storage.set (
'met:year-ct1' ,
0 )
grp.write (
'Ενέργεια τρέχοντα έτους Τ1 (kWh)' ,
0 )
storage.set (
'met:year-pt2' ,
yct2 +
delta )
grp.write (
'Ενέργεια προηγούμενου έτους Τ2 (kWh)' ,
yct2 +
delta )
storage.set (
'met:year-ct2' ,
0 )
grp.write (
'Ενέργεια τρέχοντα έτους Τ2 (kWh)' ,
0 )
storage.set (
'met:month-pt' ,
mct +
delta )
grp.write (
'Ενέργεια προηγούμενου μήνα συνολικά (kWh)' ,
mct +
delta )
storage.set (
'met:month-ct' ,
0 )
grp.write (
'Ενέργεια τρέχοντα μήνα συνολικά (kWh)' ,
0 )
storage.set (
'met:month-pt1' ,
mct1 +
delta )
grp.write (
'Ενέργεια προηγούμενου μήνα Τ1 (kWh)' ,
mct1 +
delta )
storage.set (
'met:month-ct1' ,
0 )
grp.write (
'Ενέργεια τρέχοντα μήνα Τ1 (kWh)' ,
0 )
storage.set (
'met:month-pt2' ,
mct2 +
delta )
grp.write (
'Ενέργεια προηγούμενου μήνα Τ2 (kWh)' ,
mct2 +
delta )
storage.set (
'met:month-ct2' ,
0 )
grp.write (
'Ενέργεια τρέχοντα μήνα Τ2 (kWh)' ,
0 )
storage.set (
'met:day-pt' ,
dayct +
delta )
grp.write (
'Ενέργεια προηγούμενης ημέρας συνολικά (kWh)' ,
dayct +
delta )
storage.set (
'met:day-ct' ,
0 )
grp.write (
'Ενέργεια τρέχουσας ημέρας συνολικά (kWh)' ,
0 )
storage.set (
'met:day-pt1' ,
dayct1 +
delta )
grp.write (
'Ενέργεια προηγούμενης ημέρας Τ1 (kWh)' ,
dayct1 +
delta )
storage.set (
'met:day-ct1' ,
0 )
grp.write (
'Ενέργεια τρέχουσας ημέρας Τ1 (kWh)' ,
0 )
storage.set (
'met:day-pt2' ,
dayct2 +
delta )
grp.write (
'Ενέργεια προηγούμενης ημέρας Τ2 (kWh)' ,
dayct2 +
delta )
storage.set (
'met:day-ct2' ,
0 )
grp.write (
'Ενέργεια τρέχουσας ημέρας Τ2 (kWh)' ,
0 )
elseif now.day ==
1 and now.hour ==
0 and now.min <
5 then
alert (
'Reseting Monthly, Daily energy counters' )
grp.write (
true )
storage.set (
'met:month-pt' ,
mct +
delta )
grp.write (
mct +
delta )
storage.set (
'met:month-ct' ,
0 )
grp.write (
0 )
storage.set (
'met:month-pt1' ,
mct1 +
delta )
grp.write (
mct1 +
delta )
storage.set (
'met:month-ct1' ,
0 )
grp.write (
0 )
storage.set (
'met:month-pt2' ,
mct2 +
delta )
grp.write (
mct2 +
delta )
storage.set (
'met:month-ct2' ,
0 )
grp.write (
0 )
storage.set (
'met:day-pt' ,
dayct +
delta )
grp.write (
dayct +
delta )
storage.set (
'met:day-ct' ,
0 )
grp.write (
0 )
storage.set (
'met:day-pt1' ,
dayct1 +
delta )
grp.write (
dayct1 +
delta )
storage.set (
'met:day-ct1' ,
0 )
grp.write (
0 )
storage.set (
'met:day-pt2' ,
dayct2 +
delta )
grp.write (
dayct2 +
delta )
storage.set (
'met:day-ct2' ,
0 )
grp.write (
0 )
elseif now.hour ==
0 and now.min <
5 then
alert (
'Reseting Daily energy counters' )
grp.write (
true )
storage.set (
'met:day-pt' ,
dayct +
delta )
grp.write (
dayct +
delta )
storage.set (
'met:day-ct' ,
0 )
grp.write (
0 )
storage.set (
'met:day-pt1' ,
dayct1 +
delta )
grp.write (
dayct1 +
delta )
storage.set (
'met:day-ct1' ,
0 )
grp.write (
0 )
storage.set (
'met:day-pt2' ,
dayct2 +
delta )
grp.write (
dayct2 +
delta )
storage.set (
'met:day-ct2' ,
0 )
grp.write (
0 )
elseif delta >=
0.2 then
tariff =
grp.getvalue (
'Τρέχον τιμολόγιο' )
storage.set (
'met:pt' ,
metpt +
delta )
storage.set (
'met:year-ct' ,
yct +
delta )
grp.write (
yct +
delta )
storage.set (
'met:month-ct' ,
mct +
delta )
grp.write (
mct +
delta )
storage.set (
'met:week-ct' ,
wct +
delta )
grp.write (
'Ενέργεια τρέχουσας εβδομάδας συνολικά (kWh)' ,
wct +
delta )
storage.set (
'met:day-ct' ,
dayct +
delta )
grp.write (
dayct +
delta )
storage.set (
'met:period-ct' ,
pct +
delta )
grp.write (
'Ενέργεια τρέχουσας περιόδου συνολικά (kWh)' ,
pct +
delta )
if tariff ==
2 then
storage.set (
'met:year-ct2' ,
yct2 +
delta )
grp.write (
yct2 +
delta )
storage.set (
'met:month-ct2' ,
mct2 +
delta )
grp.write (
mct2 +
delta )
storage.set (
'met:week-ct2' ,
wct2 +
delta )
grp.write (
'Ενέργεια τρέχουσας εβδομάδας Τ2 (kWh)' ,
wct2 +
delta )
storage.set (
'met:day-ct2' ,
dayct2 +
delta )
grp.write (
dayct2 +
delta )
storage.set (
'met:period-ct2' ,
pct2 +
delta )
grp.write (
'Ενέργεια τρέχουσας περιόδου Τ2 (kWh)' ,
pct2 +
delta )
storage.set (
'met:year-ct1' ,
yct1 +
delta )
grp.write (
yct1 +
delta )
storage.set (
'met:month-ct1' ,
mct1 +
delta )
grp.write (
mct1 +
delta )
storage.set (
'met:week-ct1' ,
wct1 +
delta )
grp.write (
'Ενέργεια τρέχουσας εβδομάδας Τ1 (kWh)' ,
wct1 +
delta )
storage.set (
'met:day-ct1' ,
dayct1 +
delta )
grp.write (
dayct1 +
delta )
storage.set (
'met:period-ct1' ,
pct1 +
delta )
grp.write (
'Ενέργεια τρέχουσας περιόδου Τ1 (kWh)' ,
pct1 +
delta )
if now.wday ==
1 and now.hour ==
0 and now.min <
5 then
alert (
'Reseting Weekly energy counters' )
storage.set (
'met:week-pt' ,
wct +
delta )
grp.write (
'Ενέργεια προηγούμενης εβδομάδας συνολικά (kWh)' ,
wct +
delta )
storage.set (
'met:week-pt1' ,
wct1 +
delta )
grp.write (
'Ενέργεια προηγούμενης εβδομάδας Τ1 (kWh)' ,
wct1 +
delta )
storage.set (
'met:week-pt2' ,
wct2 +
delta )
grp.write (
'Ενέργεια προηγούμενης εβδομάδας Τ2 (kWh)' ,
wct2 +
delta )
storage.set (
'met:week-ct' ,
0 )
grp.write (
0 )
storage.set (
'met:week-ct1' ,
0 )
grp.write (
0 )
storage.set (
'met:week-ct2' ,
0 )
grp.write (
0 )
Threads: 9
NICE, tanx!
As you say, then I have a starting point.
I would never had figured that out my self....
GIA
Best Regards
NewBee to wiser