Hi we got a customer with a Spacelynk that is dead. No light, maybe due to lightning.
We got at Logic Machine LM5Lp2 here that is supposed to be used at another site later this month. Can this be used at the site instead? Can I take the memory card and copy its content over or do I have to use an old backup?
Thanks for quick response
on the site knx is used,
there are also 2 hvac on modbus tcp and a PAS600(schneider) with 10 energy measurements
2 hvac on modbus rtu, a net measeurement(schneider) and earth leak instrument on modbus rtu
We got at Logic Machine LM5Lp2 here that is supposed to be used at another site later this month. Can this be used at the site instead? Can I take the memory card and copy its content over or do I have to use an old backup?
Thanks for quick response