This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Daikin FWECSA - write multiple coils and registers
#1
Hi everyone,

we've a problem with writing coils and register on a FWECSA Daikin board.

Reading through the classic json profile was good, but writing is not possible.

From the manufacturer's specifications we see the only supported fuinction codes are 15 and 16 , respectively write multiple coils and holding registers.

There is a way to write by json this values or a valid alternative solution ???

Tks in advance for your help
Reply
#2
See this: https://forum.logicmachine.net/showthrea...2#pid23482
Reply
#3
(27.01.2022, 12:09)admin Wrote: See this: https://forum.logicmachine.net/showthrea...2#pid23482

Tks Admin for your help.

Unfortunately I still can't write to coils in multiple mode.

Hope these screenshot could help us to best investigate.

Our goal is to write only the on/off (coil) and setpoint (holding reg.)

Tks again for all

Attached Files Thumbnail(s)
           
Reply
#4
Post your profile. Have you created the device again from scratch after uploading new profile?
Reply
#5
What happened in the end? We can't even write via modbus poll. Reads all right
Reply
#6
It only supports "write multiple" function. Writing to a single coil or register won't work unless "write multiple" is used.
Reply