kWh modbus to KNX convertion?
Hello everyone.
I've been using this code to convert an int16 modbus to an float16 knx.
    {       "address": 52,       "datatype": "int16",       "bus_datatype": "float16",       "name": "Total import kWh",       "value_multiplier": 0.1,       "type": "register"     },
it has been working flawless until the total kwh counter reached 3276.7 kwh.
Then it stopped working.
I prosume that the problem is that i run out of data in the 16 bit signed integer.
Then I tried to change the datatype to int32 an the bus_datatype to 14 (4-byte floating point).
But still no succes.
Any sugestions on what to do to get the propper readout in KNX?
The last code I tried is copied from another modbus profile for a powermeter:
    {       "address": 52,       "read_count":20,       "read_offset":2,       "datatype": "float32",       "bus_datatype": "14",       "name": "Total import kWh",       "value_multiplier": 0.1,       "type": "register"     },
The powermeter I use is a Carlo Gavazzi EM340.
Link to modbus manual: https://gavazzi.se/app/uploads/2020/11/e...340_cp.pdf
datatype must be set to int32. You might need use a different read_swap. Use Read test to find correct parameters.
(25.04.2023, 08:05)admin Wrote: datatype must be set to int32. You might need use a different read_swap. Use Read test to find correct parameters.
Can you specify the read test? How do I do that?
Read test is in the Modbus tab / bottom toolbar.
Okay, i've done the read test, and it has to be set as follows:
Read Swap: None (ABCD)
Datatype: int32
How do I specify the readswap in the .json file? Smile
Add "read_swap":"n" to your profile entry. It is all described here: https://openrb.com/docs/modbus.htm