11.10.2023, 13:38
Hi, i have a SpaceLynk communicating with two ventilation systems and now bacnet isnt behaving.
If i change the value of an object, the value shows up in the ventilation controller within seconds.
The controller then changes the status value to the new value.
I then expect the status values to show up in the SpaceLynk.
They did come through for a while, although not matching the "change of value" settings.
Now they have completly stopped sending, and i havent gotten any new values for the last 15 hours.
We also have the same ventilation controller at a different location being ran by an LM and the bacnet add-on.
There it gets the values everytime we scan, and every time we run the script.
So we're left believing its the bacnet client.
We're gonna have a tech out next week to check the network and use a standalone pc to check the bacnet.
We want to verify that the ventilation systems are communicating correctly and isolate what the problem is.
I raised an issue with Schneider support, where a ticket was made, but thus far no follow up.
So my questions are:
Is there a way to force-read with the spacelynk bacnet client?
Is it correct that the LM bacnet add-ons does not work with the spacelynk ?
Anyone have any other suggestions
If i change the value of an object, the value shows up in the ventilation controller within seconds.
The controller then changes the status value to the new value.
I then expect the status values to show up in the SpaceLynk.
They did come through for a while, although not matching the "change of value" settings.
Now they have completly stopped sending, and i havent gotten any new values for the last 15 hours.
We also have the same ventilation controller at a different location being ran by an LM and the bacnet add-on.
There it gets the values everytime we scan, and every time we run the script.
So we're left believing its the bacnet client.
We're gonna have a tech out next week to check the network and use a standalone pc to check the bacnet.
We want to verify that the ventilation systems are communicating correctly and isolate what the problem is.
I raised an issue with Schneider support, where a ticket was made, but thus far no follow up.
So my questions are:
Is there a way to force-read with the spacelynk bacnet client?
Is it correct that the LM bacnet add-ons does not work with the spacelynk ?
Anyone have any other suggestions