Alert Manager
#81
You can check the structure of the Alerts manager data using the Storage viewer app. But if you modify this data via a script the client won't see these changes unless a reload is performed.
It's only possible when the alert manager is loaded into an frame in the visu by using this custom JS:
$(function(){
   $(document).ready(function() {
      var f= $('iframe');
      f.load(function(){
            grp.listen('1/1/1', function(object, state) {
               if (state == 'value' && object.value == true ){
                  f.contents().find('#AcknowledgeButton').click();
            }, true);
Hi, I have used this app in the past but I have noticed that I have no more access to this alert manager in Schneider Spacelynk.
Where could I find the latest version of this app ?
Thank you
https://forum.logicmachine.net/showthrea...3#pid22783
I have written this script for surveillance of alarms. It will only generate one alarm if an Object is not updated within a range of time. You can use it as Resident or Scheduled Script. It takes every object with the tag "Alarm". Change the "controlltime" to your desire.
--This script is for Object surveillance passivley with the updatetime property
--Alarms will be updated on change!
alarms = grp.tag('Alarm') --add the Tag or Tags of the Object that need surveillance
controlltime = 30 --Allowed Time between recieved Telegramms in Seconds
--initializing Tables for Alarming
currentstate = {}
previousstate = storage.get("previousstate") or {}
now = os.time()
--Iteration throgh the alarms Table to get the update time of every Object
for index, alarm in ipairs(alarms) do
    lastrecieved = alarm.updatetime
    local online
    --calculating the Timedelta and comparing it with our Variable
    if (now - lastrecieved) > controlltime then
        online = false
        online = true
    -- Store the current status in the currentstatus table
    currentstate[alarm.id] = {id = alarm.id, comment = alarm.comment, online = online}
    -- Compare the current status with the previous status
    if previousstate[alarm.id] == nil or currentstate[alarm.id].online ~= previousstate[alarm.id].online then
        if not currentstate[alarm.id].online then
            alert("Alarm " .. currentstate[alarm.id].comment .. " nicht verfügbar")
                  alert("Alarm " ..currentstate[alarm.id].comment .. " verfügbar")
-- Log the current status
-- log(currentstate)
-- Save the current status to persistent storage as previous status
storage.set("previousstate", currentstate)
And this script that will actively send a read request to check if alarms are still available. It will take every objekt with the tag "Alarm". This is designed to be used as resedent or scheduled script.
-- Variables as Tag
currentstatus = {}
-- Iterate over all alarms
    value, responding = grp.readvalue(alarm.address, readtimeout)
    local online
    if responding == "timeout" then
        online = false
        online = true
    currentstatus[alarm.id] = {id = alarm.id, name = alarm.name, online = online}
    if previousstate[alarm.id] == nil or currentstatus[alarm.id].online ~= previousstate[alarm.id].online then
        if not currentstatus[alarm.id].online then
            alert("Alarm " .. currentstatus[alarm.id].name .. " nicht verfügbar")
--log(currentstatus)
storage.set("previousstate", currentstatus)