Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
Hello,
I tried to start using LM as a router in KNX but I've found problems.
I've connected 2 LMs as a routers: LM Reactor V3 and LM5. Firstly I've tried to use devices with not upgraded version and after current.
2 routers with addresses 1.2.0 (192.168.2.25) and 1.3.0 (192.168.2.23) connected in TP Link Router (192.168.2.1).
In 1.2 line there is only device: 1 input module from Siemens.
In 1.3 line there is also only 1 device: 4in/out analog module from MDT.
I want program firstly addresses but I see no device in programming mode. When I change connection type to TP-UART I see device in programming mode. How should I connect LM or configure it to work as a router?
The same situation is with sending group addresses. When I send value in LM Object tab to device which is connected to the LM and is routed by this LM telegram is not reaching the device but when I change LM mode to TP-UART all works fine and the device sends feedback and output is set to specific value.
Done is better than perfect
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
Routing on LM can only be used for group communication (this is done for security reasons). If your LM is connected to KNX TP you must set connection mode to TP-UART. Keep IP features enabled and routing will work as well. For TP device programming you need to connect to each LM via tunneling.
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
(31.08.2018, 08:36)admin Wrote: Routing on LM can only be used for group communication (this is done for security reasons). If your LM is connected to KNX TP you must set connection mode to TP-UART. Keep IP features enabled and routing will work as well. For TP device programming you need to connect to each LM via tunneling.
So I must change connection mode on LM to do this? On TP-UART mode does filtering works?
But IP Routing not working also for group commnication! When I replace LM via MDT router with same configuration all is good but on LM with IP Routing configuration communication is only on IP side but not on TP. On TP-UART it is. So I think there is some very important bug in IP Router.
Done is better than perfect
Posts: 4643
Threads: 24
Joined: Aug 2017
Reputation:
207
Juts use TP-UART mode, you could also make HW factory reset and it would work out of the box
------------------------------
Ctrl+F5
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
If you set connection mode to IP routing then KNX/TP will not work. This is only useful for installations without TP or when a central LM is used.
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
03.09.2018, 06:28
(This post was last modified: 03.09.2018, 06:35 by buuuudzik.)
Could you describe what all functions means with some diagrams and some examples how use LM as a device also for programming. Because I see that this is sometimes different to other normal KNX router, because normally IP Routing or KNXnet/IP what was recent name of this function normally works that telegrams are filtered between IP<->TP and you told that in such connection TP is switched off so this is a big difference. I think it should have also switch in settings programming on/off because this is a big lack and uncomfortable and for secure reasons I can also do some passwiord in ETS for devices or use KNX Secure or encrypted communication between LMs.
Done is better than perfect
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
If you have a physical TP connection, set mode to TP-UART. IP features must be enabled for routing and tunneling to work. If you set connection mode to routing or tunneling then LM will just ignore TP completely.
Our security implementation differs from standard KNX (because it's too complex and bloated as most things in KNX world). Tunneling will be disabled if only secure connections are allowed.
If you need to program devices, set mode to TP-UART, keep IP features enabled and connect to each LM directly via tunneling. There's no other way to do this.
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
So now only from curiousity can I connect LM to other KNX IP Router which use KNX Secure?
Done is better than perfect
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
No, right now secure connections can be created only between LMs.
Posts: 4643
Threads: 24
Joined: Aug 2017
Reputation:
207
No change here
------------------------------
Ctrl+F5