This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Error log - Modbus
#16
Hi Erwin, hi Danielsen,

May I suggest you test I add two bus polarization resistors ?
https://www.schneider-electric.fr/fr/faqs/FA22821/

I have not tested this solution yet, but it has been indicated recently to me by the Schneider Electric Customer Care Center.

Note: I had the same CRC problem with a Modbus iEM3155 on HomeLYnk, but I solved 90% of this malfunction by just increasing the POL and the tiemout a little bit.

BR,
Dominique
Reply


Messages In This Thread
Error log - Modbus - by Mr.D - 24.01.2018, 18:15
RE: Error log - Modbus - by admin - 25.01.2018, 07:27
RE: Error log - Modbus - by Mr.D - 25.01.2018, 08:06
RE: Error log - Modbus - by Daniel - 25.01.2018, 12:00
RE: Error log - Modbus - by Mr.D - 25.01.2018, 16:49
RE: Error log - Modbus - by Daniel - 25.01.2018, 16:54
RE: Error log - Modbus - by Mr.D - 25.01.2018, 19:51
RE: Error log - Modbus - by Mr.D - 27.01.2018, 12:17
RE: Error log - Modbus - by Mr.D - 28.01.2018, 09:55
RE: Error log - Modbus - by Mr.D - 29.01.2018, 18:46
RE: Error log - Modbus - by Mr.D - 29.01.2018, 20:25
RE: Error log - Modbus - by SigmaTec - 01.02.2018, 17:09
RE: Error log - Modbus - by Mr.D - 13.03.2018, 13:07
RE: Error log - Modbus - by sx3 - 18.04.2018, 12:01
RE: Error log - Modbus - by mlaudren - 18.04.2018, 21:50
RE: Error log - Modbus - by iJAF - 17.07.2019, 11:48

Forum Jump: