This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm whether you accept or reject these cookies being set.

Bacnet status flags
#21
Overridden flag is set to true when there's a value with higher or equal to pre-set priority is written from BACnet side. It is set false after start-up.

Out-of-service flag can only be set from BACnet side and remains active until BACnet server on LM is restarted.
Reply
#22
(19.02.2018, 13:50)admin Wrote: Overridden flag is set to true when there's a value with higher priority is set from BACnet side. It is set false after start-up and it will revert to false if NULL is written to previously set array item with higher priority.

Out-of-service flag can only be set from BACnet side and remains active until BACnet server on LM is restarted.

Hi Admin,

This is correct, but we always write to a priority level (1-16) so after first written value the override flag is active, only when we could write directly to value property we could avoid it.
 
BR,

Erwin
Reply
#23
Yes, that's correct, I've edited my original post Smile
Reply
#24
Hi to all, 

As i realized there is not a clear answer why the status flag overridden is active at LM each time a COV service is active.

We also facing the same strange reaction for every AVAL object is subscribed to Siemens Desigo CC software. This only happens with LM and not with Siemens N 143/01 device which is working normally for the same purpose. We use both devices to integrate several KNX networks.

Any information will be helpful.
Reply
#25
(16.03.2018, 16:40)Livadi77 Wrote: Hi to all, 

As i realized there is not a clear answer why the status flag overridden is active at LM each time a COV service is active.

We also facing the same strange reaction for every AVAL object is subscribed to Siemens Desigo CC software. This only happens with LM and not with Siemens N 143/01 device which is working normally for the same purpose. We use both devices to integrate several KNX networks.

Any information will be helpful.

Are you using the Siemens Xworks CFC or are you taking the points directly into CC?
Reply
#26
(08.04.2019, 07:23)Tokatubs Wrote:
(16.03.2018, 16:40)Livadi77 Wrote: Hi to all, 

As i realized there is not a clear answer why the status flag overridden is active at LM each time a COV service is active.

We also facing the same strange reaction for every AVAL object is subscribed to Siemens Desigo CC software. This only happens with LM and not with Siemens N 143/01 device which is working normally for the same purpose. We use both devices to integrate several KNX networks.

Any information will be helpful.

Are you using the Siemens Xworks CFC or are you taking the points directly into CC?

Directly to CC. There is no issue with CFC.
Reply
#27
Hi
Can you update bacnet with this package?
New CPU
http://dl.openrb.com/pkg/bacnet_20190403_imx6.ipk
OLD CPU
http://dl.openrb.com/pkg/bacnet_20190403_mxs.ipk
BR
Reply
#28
(15.04.2019, 14:18)Daniel. Wrote: Hi
Can you update bacnet with this package?
New CPU
http://dl.openrb.com/pkg/bacnet_20190403_imx6.ipk
OLD CPU
http://dl.openrb.com/pkg/bacnet_20190403_mxs.ipk
BR

Thank you. I will try to update the device as soon as possible and of course i will inform you about the reaction to our issue.
Reply
#29
Hi,
Im having this statusflag problem with a spacelynk to ecostruxure, is there a solution ?

Best regards
/P
Reply