This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet status flags
#2
Hi

Check to which priority array your scada is writing to. LM by default will write to 16 but you can change it. If your scada is writing to higher priority then yes it will be overridden and all values from LM will be in PA16 but ignored by Present Value.
Yo can clear priority array on LM by simply disabling bacnet server and enabling it again.

First exported 256 objects will have COV. If you have more then the rest must be pooled. Proper bacnet client will just deal with it out of the box.

BR
------------------------------
Ctrl+F5
Reply


Messages In This Thread
Bacnet status flags - by eirik - 14.02.2018, 07:45
RE: Bacnet status flags - by Daniel - 14.02.2018, 08:33
RE: Bacnet status flags - by eirik - 14.02.2018, 09:06
RE: Bacnet status flags - by Daniel - 14.02.2018, 09:10
RE: Bacnet status flags - by eirik - 15.02.2018, 19:00
RE: Bacnet status flags - by Daniel - 15.02.2018, 19:06
RE: Bacnet status flags - by Trond Hoyem - 13.05.2020, 11:04
RE: Bacnet status flags - by eirik - 15.02.2018, 21:24
RE: Bacnet status flags - by Daniel - 15.02.2018, 22:33
RE: Bacnet status flags - by eirik - 16.02.2018, 07:05
RE: Bacnet status flags - by eirik - 18.02.2018, 15:09
RE: Bacnet status flags - by Daniel - 18.02.2018, 16:26
RE: Bacnet status flags - by eirik - 18.02.2018, 17:23
RE: Bacnet status flags - by admin - 18.02.2018, 18:57
RE: Bacnet status flags - by eirik - 19.02.2018, 06:14
RE: Bacnet status flags - by admin - 19.02.2018, 07:07
RE: Bacnet status flags - by eirik - 19.02.2018, 08:06
RE: Bacnet status flags - by eirik - 19.02.2018, 13:40
RE: Bacnet status flags - by admin - 19.02.2018, 13:50
RE: Bacnet status flags - by admin - 19.02.2018, 14:22
RE: Bacnet status flags - by Livadi77 - 16.03.2018, 16:40
RE: Bacnet status flags - by Tokatubs - 08.04.2019, 07:23
RE: Bacnet status flags - by Livadi77 - 15.04.2019, 14:14
RE: Bacnet status flags - by domotiqa - 16.10.2019, 18:41
RE: Bacnet status flags - by Livadi77 - 17.10.2019, 05:53
RE: Bacnet status flags - by Daniel - 15.04.2019, 14:18
RE: Bacnet status flags - by Livadi77 - 18.04.2019, 20:54
RE: Bacnet status flags - by Livadi77 - 14.05.2020, 06:58
RE: Bacnet status flags - by stavros - 12.09.2019, 08:27
RE: Bacnet status flags - by Polkaz - 23.05.2019, 18:45
RE: Bacnet status flags - by Daniel - 12.09.2019, 08:49
RE: Bacnet status flags - by domotiqa - 17.10.2019, 11:16
RE: Bacnet status flags - by domotiqa - 25.10.2019, 06:10

Forum Jump: