This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet status flags
#8
Hi 
I've checked the priority array. All other prioritys are set to nil.
It's only values in array 16.

I'm also testing to change the relinquish default, but get an write access denied.
This is tested with both SCADA and YABE.
It also appear an write access denied when I try to change the setpoint on a KNX-thermostat.
But the object in the LM5 updates, also on the KNX-bus.

Eirik 
Reply


Messages In This Thread
Bacnet status flags - by eirik - 14.02.2018, 07:45
RE: Bacnet status flags - by Daniel - 14.02.2018, 08:33
RE: Bacnet status flags - by eirik - 14.02.2018, 09:06
RE: Bacnet status flags - by Daniel - 14.02.2018, 09:10
RE: Bacnet status flags - by eirik - 15.02.2018, 19:00
RE: Bacnet status flags - by Daniel - 15.02.2018, 19:06
RE: Bacnet status flags - by Trond Hoyem - 13.05.2020, 11:04
RE: Bacnet status flags - by eirik - 15.02.2018, 21:24
RE: Bacnet status flags - by Daniel - 15.02.2018, 22:33
RE: Bacnet status flags - by eirik - 16.02.2018, 07:05
RE: Bacnet status flags - by eirik - 18.02.2018, 15:09
RE: Bacnet status flags - by Daniel - 18.02.2018, 16:26
RE: Bacnet status flags - by eirik - 18.02.2018, 17:23
RE: Bacnet status flags - by admin - 18.02.2018, 18:57
RE: Bacnet status flags - by eirik - 19.02.2018, 06:14
RE: Bacnet status flags - by admin - 19.02.2018, 07:07
RE: Bacnet status flags - by eirik - 19.02.2018, 08:06
RE: Bacnet status flags - by eirik - 19.02.2018, 13:40
RE: Bacnet status flags - by admin - 19.02.2018, 13:50
RE: Bacnet status flags - by admin - 19.02.2018, 14:22
RE: Bacnet status flags - by Livadi77 - 16.03.2018, 16:40
RE: Bacnet status flags - by Tokatubs - 08.04.2019, 07:23
RE: Bacnet status flags - by Livadi77 - 15.04.2019, 14:14
RE: Bacnet status flags - by domotiqa - 16.10.2019, 18:41
RE: Bacnet status flags - by Livadi77 - 17.10.2019, 05:53
RE: Bacnet status flags - by Daniel - 15.04.2019, 14:18
RE: Bacnet status flags - by Livadi77 - 18.04.2019, 20:54
RE: Bacnet status flags - by Livadi77 - 14.05.2020, 06:58
RE: Bacnet status flags - by stavros - 12.09.2019, 08:27
RE: Bacnet status flags - by Polkaz - 23.05.2019, 18:45
RE: Bacnet status flags - by Daniel - 12.09.2019, 08:49
RE: Bacnet status flags - by domotiqa - 17.10.2019, 11:16
RE: Bacnet status flags - by domotiqa - 25.10.2019, 06:10