This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet status flags
#22
(19.02.2018, 13:50)admin Wrote: Overridden flag is set to true when there's a value with higher priority is set from BACnet side. It is set false after start-up and it will revert to false if NULL is written to previously set array item with higher priority.

Out-of-service flag can only be set from BACnet side and remains active until BACnet server on LM is restarted.

Hi Admin,

This is correct, but we always write to a priority level (1-16) so after first written value the override flag is active, only when we could write directly to value property we could avoid it.
 
BR,

Erwin
Reply


Messages In This Thread
Bacnet status flags - by eirik - 14.02.2018, 07:45
RE: Bacnet status flags - by Daniel - 14.02.2018, 08:33
RE: Bacnet status flags - by eirik - 14.02.2018, 09:06
RE: Bacnet status flags - by Daniel - 14.02.2018, 09:10
RE: Bacnet status flags - by eirik - 15.02.2018, 19:00
RE: Bacnet status flags - by Daniel - 15.02.2018, 19:06
RE: Bacnet status flags - by Trond Hoyem - 13.05.2020, 11:04
RE: Bacnet status flags - by eirik - 15.02.2018, 21:24
RE: Bacnet status flags - by Daniel - 15.02.2018, 22:33
RE: Bacnet status flags - by eirik - 16.02.2018, 07:05
RE: Bacnet status flags - by eirik - 18.02.2018, 15:09
RE: Bacnet status flags - by Daniel - 18.02.2018, 16:26
RE: Bacnet status flags - by eirik - 18.02.2018, 17:23
RE: Bacnet status flags - by admin - 18.02.2018, 18:57
RE: Bacnet status flags - by eirik - 19.02.2018, 06:14
RE: Bacnet status flags - by admin - 19.02.2018, 07:07
RE: Bacnet status flags - by eirik - 19.02.2018, 08:06
RE: Bacnet status flags - by eirik - 19.02.2018, 13:40
RE: Bacnet status flags - by admin - 19.02.2018, 13:50
RE: Bacnet status flags - by Erwin van der Zwart - 19.02.2018, 14:20
RE: Bacnet status flags - by admin - 19.02.2018, 14:22
RE: Bacnet status flags - by Livadi77 - 16.03.2018, 16:40
RE: Bacnet status flags - by Tokatubs - 08.04.2019, 07:23
RE: Bacnet status flags - by Livadi77 - 15.04.2019, 14:14
RE: Bacnet status flags - by domotiqa - 16.10.2019, 18:41
RE: Bacnet status flags - by Livadi77 - 17.10.2019, 05:53
RE: Bacnet status flags - by Daniel - 15.04.2019, 14:18
RE: Bacnet status flags - by Livadi77 - 18.04.2019, 20:54
RE: Bacnet status flags - by Livadi77 - 14.05.2020, 06:58
RE: Bacnet status flags - by stavros - 12.09.2019, 08:27
RE: Bacnet status flags - by Polkaz - 23.05.2019, 18:45
RE: Bacnet status flags - by Daniel - 12.09.2019, 08:49
RE: Bacnet status flags - by domotiqa - 17.10.2019, 11:16
RE: Bacnet status flags - by domotiqa - 25.10.2019, 06:10

Forum Jump: