Advice on hanging Resident script (suspect storage get/set)
Hi, i'm experiencing some kind of hang/blocking/locking when this script runs for a few days.
The script runs as a Resident script every minute, but suddenly it stops. I try to disable, re- enable but without any success.
Then, when I alter the storage key ('3_3_15_vent_effect') to e.g. '3_3_15_vent_effect_1' it runs fine for some time (days?).
Should I safeguard the storage get/set in some way? I'm I missing something obvious here?
deltaThreshold = 0.015 t1 = grp.getvalue('3/3/10') t2 = grp.getvalue('3/3/11') t3 = grp.getvalue('3/3/14') -- Calc. effect effect = (t1 - t3) / (t2 - t3) prev_effect = storage.get('3_3_15_vent_effect', 0) effectDelta = math.abs(prev_effect - effect) -- Write to KNX buss if Delta > Treshold if effectDelta > deltaThreshold then  grp.write('3/3/15', effect)    -- Store Calculated effect  storage.set('3_3_15_vent_effect', effect)    log("New reading - Effect prev.=" .. prev_effect .. " New = " .. effect) end
About the script: Calculate the effect of a heat recovery unit. Input values are collected from ModBus interface on LM (no need to do a grp.read()). I don't want to flood the KNX buss by writing every calculation, therefore the delta calculation.
Alternative approaches are welcome...
_
Ole A.
You don't need storage in a resident script like this. All variables will keep their values after each call, but will be nil on first script run, so you have to check for that. Sending a telegram once a minute is not a problem. You should use grp.update instead of grp.write if you don't need this value on KNX/TP bus.
Thank you for clarifying. Didn't realize variables were persisted at this level.
Needs the values on the bus, and as we know, "he" is a grumpy ~100year old man you shouldn’t nag too often Wink
_
Ole A.
I did this another way, I also use the modbus to collect from Systemair unit as well as my 1 wire sensors in the hc unit to collect values.
I have made a script that runs on event change. That means if one of the three values are updated then the script runs. Works as a charmSmile results last 24 hours can be viewed on www.passivpluss.no Smile