if (two conditions) then
I have made a script with two conditions that need to be fulfilled before doing something. I have tried everything bt it is not working. There are no syntax errors now and I disable/enable every time I save scripts just to be sure.
The script reads a value from a illumination sensor and status from a light object. Then it compares the two and writes to the same light object. Here it is:
illumivalue = grp.getvalue('32/1/3')
switchvalue = grp.getvalue('0/4/10')
if (illumivalue <= 5 and switchvalue == 0) then
  grp.write('0/4/10',1)
elseif (illumivalue >= 5 and switchvalue == 1)
  then grp.write('0/4/10',0)
(11.03.2018, 00:04)02dag Wrote: Hi,
Change this line:
if (illumivalue <= 5 and switchvalue == false) then
Done is better than perfect
Change this line:
Thank you very much. This worked, but I am puzzled. I thought that you could use both 0/1 or /true/false for things like this? Never thought of the latter for this script though.
Change this line:
You can check that type(false) is 'boolean' and type(0) is 'number'. If you aren't sure of type of variable you can use toboolean function. Check this:
log(type(false))
log(type(0))
log(type(toboolean(0)))
true/false or 1/0 does not matter for writing, when comparing something it (offcourse) cannot be both (:
Tip: If result of a condition is not what you expect, log the variables to see what is going on..
