This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet for dummies
#3
(07.11.2018, 22:04)Erwin van der Zwart Wrote: Hi,

That would require the BACnet client package. At the moment the client is script based without a GUI to map the BACnet objects to KNX. Also not all BACnet object types are supported. (like BACnet trends, BACnet schedulers and BACnet alarms or notification class) and COV is not supported in the client so you need to poll the objects for changes.

Keep in mind that you can’t use the server and client at the same time due to used ports by both.

In case of a BMS i would recommand the use of the server as it has COV and can handle a lot more objects. Bindings/mapping needs to be done in the BMS in that case.

BR,

Erwin

I installed the package from her. http://openrb.com/logicmachine-as-bacnet-client/

But i did not really get where to write the script from the examples in the article. 

So if i understand correct i cant export from the knx to bacnet and at the same time send commands from bacnet to knx. In that case i would need two LM`s.
Reply


Messages In This Thread
Bacnet for dummies - by Tokatubs - 07.11.2018, 21:28
RE: Bacnet for dummies - by Tokatubs - 07.11.2018, 23:13
RE: Bacnet for dummies - by Tokatubs - 09.11.2018, 08:28
RE: Bacnet for dummies - by Daniel - 08.11.2018, 09:09

Forum Jump: