25.12.2018, 13:24
(This post was last modified: 26.12.2018, 02:47 by CHOUAIBOU.)
(24.12.2018, 17:00)AlexLV Wrote: I think above just copy of previous post...
Guys, can you please post here final script?? I tried to make changes mentioned but not work for me..
Hi AlexLV,
Please find bellow the working script. There was an error in the time string format.
Merry Christmas
B.R,
Chouaibou.
Code: -- ** Staircase logic with external time object and retriggering on input object Version 3.2 ** --
-- ****************************** Created by Erwin van der Zwart **************************** --
-- ************************************** SET PARAMETERS ************************************ --
-- Set output address
AddressOutput = '32/1/21' -- 01. 1 bit (boolean)
-- Set external time address (optional)
AddressExternalTime = '32/1/22' -- 07. 2 byte unsigned integer
-- Use time left indication
UseTimeLeft = true -- Set to false if no time left indication is used
-- Set feedback adress of time left indication (optional)
AddressTimeLeft = '32/1/23' -- 255 byte string
-- Set time delay (Used when external time is not available)
SetDelay = 120 -- 2 minutes
-- Seconds or Minutes
SetSec = true -- Set to false for Minutes
-- Set factor delay (Multiplies Delay)
SetFac = 1
-- Logic can be turned of by value 0
Off_by_Value_Zero = false
-- ************************************** END PARAMETERS ************************************ --
-- *************************** DON'T CHANGE ANYTHING UNDER THIS LINE ************************ --
Input_Value = event.getvalue()
if Off_by_Value_Zero == false and (Input_Value == false or Input_Value == 0) then
return
tpid = storage.get('PID:' .. _SCRIPTNAME)
if tpid == nil then
pid = os.getpid()
storage.set('PID:' .. _SCRIPTNAME, pid)
pid = os.getpid()
os.kill(tpid, signal.SIGKILL)
function Calculate_Time(StairCaseTime)
if StairCaseTime > (86400 -1) then
StairCaseTime = (86400 -1)
local hours = math.floor(StairCaseTime / 3600 % 24)
local minutes = math.floor(StairCaseTime / 60 % 60)
local seconds = math.floor(StairCaseTime % 60)
time = {
day = 0,
hour = hours,
minute = minutes,
second = seconds,
time =string.format('%02d:%02d:%02d',time.hour,time.minute,time.second)
return time
if Input_Value == true or Input_Value == 1 then
ValueExternalTime = grp.getvalue(AddressExternalTime) or SetDelay
if SetSec == true then
Multiply_Seconds = 1
Multiply_Seconds = 60
StairCaseTime = ValueExternalTime * Multiply_Seconds * SetFac
ValueOutput = grp.getvalue(AddressOutput)
if ValueOutput == false then
grp.write(AddressOutput, true)
if UseTimeLeft == true then
if StairCaseTime > 0 then
time = Calculate_Time(StairCaseTime)
grp.update(AddressTimeLeft, time)
repeat
StairCaseTime = StairCaseTime - 1
os.sleep(1)
until StairCaseTime == 0
os.sleep(StairCaseTime)
grp.write(AddressOutput, false)
elseif Input_Value == false or Input_Value == 0 then
if ValueOutput == true then
time = Calculate_Time(0)
storage.delete('PID:' .. _SCRIPTNAME)
Threads: 87
26.12.2018, 09:05
(This post was last modified: 26.12.2018, 09:06 by AlexLV.)
Chouaibou, BIG THANKS
Now it finally working!!! You just forgot insert input address, so below all should work fine
I wish to all Happy New Year
Alex
-- Set input address
AddressInput = '32/1/20 ' -- 01. 1 bit (boolean)
SetFac = 1
return
if tpid == nil then
pid = os.getpid()
pid = os.getpid()
time = {
day = 0,
hour = hours,
minute = minutes,
second = seconds,
return time
repeat
os.sleep(1)
Threads: 87
06.01.2019, 23:05
(This post was last modified: 06.01.2019, 23:06 by AlexLV.)
Hi.
How correctly reset this timer in taster key is pressed before timer finished?? If use this from script:
Off_by_Value_Zero = true
timer just stopped not resetted. If I press input key again timer just starting again. How change script?
Thank you for help.
Alex
Threads: 42
Code: blocking = grp.read('0/0/1')
Out01 = '0/0/2'
if AddressOutput == true and (blocking == true or blocking == 1) then grp.write (out01, true)
if AddressOutput == false and (blocking == true or blocking == 1) then grp.write (out01, false)
Hello, if possible I would like to include in this script one more function, it would be a block. But I can't make it work.
This script is incorrect. grp.read sends read request but does not return current value. You need to use grp.getvalue instead.
It can also be simplified like this:
Code: value = event.getvalue()
blocking = grp.getvalue('0/0/1')
if blocking then
grp.write('0/0/2', value)
In FBeditor there's Select switch > Lock out block that can be used.
Threads: 42
SetFac = 1
return
if tpid == nil then
pid = os.getpid()
pid = os.getpid()
time = {
day = 0,
hour = hours,
minute = minutes,
second = seconds,
return time
repeat
os.sleep(1)
Hi admin, thanks for your response, I need to include it in the script itself. I have tried your script and it only activates the output if the block is true, but I need if the block is true that it activates and deactivates me at the end of the time.
If you don't want to run script if blocking is set to true then simply add this to the start of your script:
Code: blocking = grp.getvalue('0/0/1')
if not blocking then
return
Threads: 42
29.01.2020, 15:47
(This post was last modified: 29.01.2020, 16:25 by davidchispas.)
(29.01.2020, 13:34)admin Wrote: If you don't want to run script if blocking is set to true then simply add this to the start of your script:
return
Thanks Admin, it works perfectly!
AddressInput = '21/1/40' -- 01. 1 bit (boolean)
AddressOutput = '1/1/40' -- 01. 1 bit (boolean)
AddressExternalTime = '55/1/4' -- 07. 2 byte unsigned integer
AddressTimeLeft = '55/1/5' -- 255 byte string
SetFac = 1
blocking = grp.getvalue('40/1/40')
return
return
if tpid == nil then
pid = os.getpid()
pid = os.getpid()
time = {
day = 0,
hour = hours,
minute = minutes,
second = seconds,
return time
repeat
os.sleep(1)
I have a small error activating the lock. If the timing is already started before blocking ... at the end of that time, send false. Is it possible to correct not send it?
Threads: 8
29.01.2020, 22:05
(This post was last modified: 29.01.2020, 22:06 by Erwin van der Zwart.)
You need to add the blocking after the kill part to make sure the previous script is killed when the new one started.
-- Set blocking address
AddressBlocking = '40/1/40'
SetFac = 1
return
if tpid == nil then
pid = os.getpid()
pid = os.getpid()
blocking = grp.getvalue(AddressBlocking)
return
time = {
day = 0,
hour = hours,
minute = minutes,
second = seconds,
return time
repeat
os.sleep(1)
Threads: 87
Hi Erwin,
this is super script  As I sent some times ago private mail to you and you recommend to me use it - I used this script, all is working wonderful  Big thanks!!! One thing is absent in your script. We can just stop it if Logic turn off = 1, but can we somehow reset time before it will end by timer? In that case we will have super timer with start/stop/blocking/reset possibilities..
Alex
Threads: 8
If you send a 1 again on the trigger object it should reset the time and start counting from start.
Threads: 87
Erwin,
Yes, I thought about such option, but I am using this at visu:
So when I stop I see remained time, if I restart it - time starts from the beginning. But I need if I reset timer - timer ends and remain time = zeros and output deactivated, before countdown finished by themselves.. Tried different ways, but not successfully to solve this idea with your script..
Threads: 42
(29.01.2020, 22:05)Erwin van der Zwart Wrote: Hi,
SetFac = 1
return
if tpid == nil then
pid = os.getpid()
pid = os.getpid()
return
time = {
day = 0,
hour = hours,
minute = minutes,
second = seconds,
return time
repeat
os.sleep(1)
Erwin Thank you so much for the correction! Now it works perfectly! It is a great script!
Threads: 17
(30.01.2020, 09:29)Erwin van der Zwart Wrote: Hi,
The count starts from begging but the output is not resends 1.
Is there something more that needs to be done for this?
Threads: 8
02.05.2020, 22:05
(This post was last modified: 02.05.2020, 22:07 by Erwin van der Zwart.)
Change line 80-83:
Code: ValueOutput = grp.getvalue(AddressOutput)
Into:
Code: grp.write(AddressOutput, true)
This way the output is not checked on state
Threads: 17
(02.05.2020, 22:05)Erwin van der Zwart Wrote: Hi,
Change line 80-83:
Into:
Erwin Yeah thanks!
Now I want to implement a Nightmode that changes the output after nightshift.
I change the outeput address to "AddressOutputDay" and added these new ones "AddressOutputNight", "NighMode" and "AddressOutputStatus".
Then changed the script like this
Code: StairCaseTime = ValueExternalTime * Multiply_Seconds * SetFac
ValueOutput = grp.getvalue(AddressOutputStatus)
if ValueOutput == false and NightMode == false then
grp.write(AddressOutputDay, true)
grp.write(AddressOutputNight, true)
But it just uses "AddressOutputNight" even if NightMode is false or true.
What is the right way of doing this?
Threads: 8
07.05.2020, 20:33
(This post was last modified: 07.05.2020, 20:34 by Erwin van der Zwart.)
I need to see the complete script as now there is no way of telling what you do wrong, i can’t see what you have declared for the night mode vars etcetera...
Threads: 17
(07.05.2020, 20:33)Erwin van der Zwart Wrote: Hi,
Erwin Here it is.
AddressInput = '5/4/1' -- 01. 1 bit (boolean)
AddressOutputDay = '32/1/38' -- 01. 1 bit (boolean)
AddressOutputNight = '32/1/41'
-- Set Status feedback of room controoled lights
AddressOutputStatus = '5/0/26'
AddressExternalTime = '5/4/2' -- 07. 2 byte unsigned integer
AddressTimeLeft = '32/1/39' -- 255 byte string
-- Set Auto address
AddressAuto = '32/1/40'
SetFac = 1
--Manuell off when sends a "0" Resets Staircase logic manually
AddressManOff = '5/0/0'
--Day/Night switchover, Night if value "1"
NightMode = '0/7/3' --01. 1 bit (boolean)
return
if tpid == nil then
pid = os.getpid()
pid = os.getpid()
auto = grp.getvalue(AddressAuto)
if not auto then
return
time = {
day = 0,
hour = hours,
minute = minutes,
second = seconds,
return time
repeat
os.sleep(1)
grp.write(AddressOutputDay, false)
if AddressManOff == false then
grp.write(StairCaseTime, 0)
grp.write(AddressInput, 0)
AddressTimeLeft:write(0,0,0)
Threads: 8
You declare NightMode = 'x/x/x' and later you compare NightMode == false, this will not work..
Use: NightMode = grp.getvalue('x/x/x')
Threads: 17
(09.05.2020, 11:44)Erwin van der Zwart Wrote: Hi,
Erwin Perfect, it did the trick! Thanks.
Is it possible to implement a script that, after staircase time the light level dims smoothly down instead of switch to 0, without changing the dim parameters in the KNX dimmer?