Controlling Temp with timer
Hi all,
I am monitoring water temperature with LM and KNX, but I need send email when current temperature is higher than "max limit" during one period of time (e.g. 60 min).
Anyone could help me? Thanks
Create an event script mapped to temperature object:
temp = event.getvalue()
curr = temp > 22
prev = storage.get('temp_over')
if curr ~= prev then
  if curr then
    storage.set('temp_time', os.time())
    storage.set('temp_notified', false)
  storage.set('temp_over', curr)
Then create a scheduled script that runs every minute to check whether e-mail needs to be sent. Change delta time if needed (60 * 60 = 1 hour in seconds).
curr = storage.get('temp_over')
notified = storage.get('temp_notified')
if curr and not notified then
  now = os.time()
  time = storage.get('temp_time', now)
  delta = now - time
  if delta > 60 * 60 then
    -- send email
    storage.set('temp_notified', true)
(15.03.2019, 08:05)admin Wrote: Create an event script mapped to temperature object:
curr = temp > 22
 if curr then
 now = os.time()
 delta = now - time
   -- send email
Thank you very much!! Script works perfectly on my LM. Is there any handbook or manual to learn advanced scripts in LUA???
Common LM/Lua functions are documented: http://openrb.com/docs/lua.htm
As for more advanced things, have a look at example in forums and on our website. There are some many possible solutions and approaches that it's just not possible to document them.
This function is very useful.
I use it to check a temperature for 5 minutes if it goes above 23 ° C so I send an email.
If possible, I would like to send an email when the temperature drops below 23 ° C.
This email must be sent only after a temperature fault and not every time the temperature is below 23 ° C.
thank you. B. R.
Event script:
curr = temp > 23
Scheduled script:
if not notified then
  now = os.time()
  delta = now - time
  if delta > 5 * 60 then
    if curr then
      text = 'temp over limit'
      text = 'temp under limit'
    -- send email