Hi,
Do you have a lot of cyclic sending devices like motion sensors and thermostats?
If not then i would concider to disabling filters in the couplers with just 3 lines as i think you will have very low traffic and filtering is not needed. So why would you make it more difficult then needed.
If you want to enable filtering then all control and feedback addresses used in the controller need to be in the tables and be passed through to the lines where they are used.
BR,