Query Object status "Thermostat Status Alert" in Mosaic
From the Mosaic Widgett, I want to control a Radiant floor, Change operating mode and raise the setpoint temperature lower.
I control the setpoint temperature, the problem is with the change of operating mode.
The question I have with "The type of object to associate in Thermostat Status Alert would be the same as Operation Mode Status?
  I have an object of a byte that gives me the general state of the controller, would this object be valid?
  Attached capture image of Mosaic and the type of Object of 1 Byte.
Thermostat widget treats status bits like this (status/alert input is 1 byte object):
Quote:Bit 0 - Mode Comfort
Bit 1 - Mode Standby
Bit 2 - Mode Night
Bit 3 - Mode Frost/heat protection
Bit 4 - Dew point alarm
Bit 5 - Heating/Cooling
Bit 6 - Controller active
Bit 7 - Frost alarm
It should work for you apart from the Dew point alarm bit.
The operation mode is done via:
• "4" = Frost/heat protection
• "3" = Night reduction
• "2" = Standby
• "1" = Comfort
Where the Thermostat status is like this:
Bit 0Comfort (1/0)
Bit 1Standby (1/0)
Bit 2Night operation (1/0)
Bit 3Frost/heat protection (1/0)
Bit 4Dewpoint alarm 1/0
Bit 5Heating (1)/cooling (0)
Bit 6Controller inactive (1/0)
Bit 7Frost alarm (1/0)
Nearly the same as in Jung I think,
This is based on SE thermostat.
(18.03.2019, 11:24)admin Wrote: Thermostat widget treats status bits like this (status/alert input is 1 byte object):
Bit 2 - Mode Night
Bit 7 - Frost alarm
Bit 0 - Mode Comfort   -Then I understand that when Bit "0" is "1" Comfort mode "on"
Bit 1 - Mode Standby   -Then I understand that when Bit "1" is "1" Stanby mode "on"
Bit 2 - Mode Night       -Then I understand that when Bit "2" is "1" Night mode "on"
Bit 3 - Mode Frost/heat protection   -Then I understand that when Bit "3" is "1" Mode Frost/heat protection "on"
 Only I have to take into account these 4 first Bit, according to this with selecting the object of my Jung thermostat would be enough, but I can not get the status in the Widget, should I do a Script?
Br
What datatype have you set for this object? It should be set to 5 (1 byte unsigned).
(18.03.2019, 14:47)pid=\12333 Wrote:What datatype have you set for this object? It should be set to 5 (1 byte unsigned).
  Object 1/0/5 is the mode of operation and object 1/0/6 should be the state
    admin
admin
Now if I get the data, this data changes depending on the bits that are active (Dewpoint alarm, Heating / cooling ....)
How can I know the operating mode status, knowing that inside the Byte it changes its value depending on the state of the controller?
  Josema
admin
  Josema
Just check which bit 0-3 is set to 1
You can use this script to decode bitmask to separate binary values: https://forum.logicmachine.net/showthrea...57#pid9757
(18.03.2019, 17:36)admin Wrote: You can use this script to decode bitmask to separate binary values: https://forum.logicmachine.net/showthrea...57#pid9757
Thank you very much for your response, I will look to see if I have understood and I am capable Once the Byte is decrypted, what will be the object for the mosaic thermostat?
 Thanks again
  Jose Ma
 I report here the solution with which I solve the problem I had to see in Mosaic 2.0 the status of the operation mode of the stay controls JUNG 4093KRMTSD.
Thanks for your help, thanks also to David that without his help he could not have done it
Where do I apply the following
 [archivo adjunto = 1269]
.txt   Script Estado Modo de Funcionamiento.txt (Size: 1.01 KB / Downloads: 7)