This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus profie Satec PM130 Plus
#4
Try this, since the resulting value has to be multiplied by 0.001, bus_datatype field has to be set to float32, but datatype field (which tells what kind of data is read from ModBus) should be set to int32.

Code:
{
   "manufacturer": "satec",
   "description": "PM",
   "mapping": [
      {
         "name": "PF_L1",
         "bus_datatype": "float32",
         "datatype": "int32",
         "type": "register",
         "value_multiplier": 0.001,
         "address": 13342
      }
   ]
}
Reply