Read with Wait function
Hello
I'm looking for a function which sends read request to KNX bus and waits for the result. The reason is I have two inputs which I need to be sure their values are actual.
This works but it's ugly because I don't check if the readings of both values were successful:
grp.read('6/4/28')
grp.read('6/4/45')
os.sleep(5)
val_a=grp.getvalue('6/4/28')
val_b=grp.getvalue('6/4/45')
Is there such
err,val_a=grp.readAndWait('6/4/28')
LM5Lp, firmware: 2018.08.22, FlashSYS v2, ARMv7 Processor rev 5 (v7l), kernel 4.4.151
Use this function:
function readresponse(alias, timeout)
  local obj, lb, ts, tu, delta, value
  obj = grp.find(alias)
  if not obj then
    return nil, 'object not found'
  timeout = timeout or 3
  lb = require('localbus').new(timeout / 10)
  lb:sethandler('groupresponse', function(event)
    if event.dst == obj.address then
      value = busdatatype.decode(event.datahex, obj.datatype)
  end)
  grp.read(obj.address)
  ts, tu = os.microtime()
  repeat
    lb:step()
    delta = os.udifftime(ts, tu)
  until value ~= nil or delta >= timeout
  if value ~= nil then
    return value
    return nil, 'timeout'
res, err = readresponse('0/0/3')
log(res, err)
Excellent as usual Admin. Thank you.
But does lb:step() do yield? Isn't the cycle utilising the CPU to 100%?
It returns once a single local bus message has been received or timeout happens. Script does not consume CPU while waiting.