Threads: 9
Hi guys...
is there a way to activate and deactivate the Modbus RTU Serial 1 by an event script?, cuz´I want to use an object for doing this from the visualization without using the administrator accountÂ
B.R
What is the use case for that?
Threads: 9
Hi admin,
I'm trying to use 2 Modbus Masters writing in KNX(The LM and an external one)reading common devices but clearly not at the same time, so the master change should be done by the final user, switching between them without getting access over the LM config. That's why I want to set up a switch in user's visualization for make this change.
B.R
Threads: 30
This is not the best approach. You should make one device talking to slave and the other two masters should exchange data in another way. LM can be also modbus slave.
Threads: 9
28.08.2019, 15:25
(This post was last modified: 28.08.2019, 15:27 by HannPark.)
Thanks Daniel,
But what happened if I had 2 masters reading same devices?, in Modbus that's imposible but...you can do it if you turn off one master when the other one is working, as I see.. that's like a redundant modbus network, that's the thing that I wanna get... it's easy from the admin account cuz' you just go to the modbus tab and disable RTU and it's done...but the tricky thing is to do it from the visualization...
Threads: 9
Thank u so much admin, it totally works!
B.R
