Datatype "Percentage difference" Mosaic.
Tried making a easier way for people to regulate the ventilation and Vav.
Then the ventilation guy could change via Mosaic instead of me, changing via Ets.
The Siemens GDB181 uses 2 setpoints for Vmin and Vmax. But these are in Ets in "percentage difference" 8.010 so i dont see that there is a datatype for this out of the box.
Like in the example above the setpoint should be 30%. But shows 3000 when choosing the 8. 2 bytes signed integer. Choosing 0-100 in visualizations parameters i guess only apply to the Visu and not mosaic?
Anyone have an idea how to change this to correct value.
What value do you receive from KNX? 3000 or 30?
I think you will need a script to convert it to % if you want it to be in this format.
(30.09.2019, 10:22)Daniel. Wrote: Hi
Reiceved from knx is 3000  yes. The datatype in Ets is 8.010 "percentage difference".
My thought in the mosaic creator also is a bit wrong. When i try a different number it goes back to 100 as max.
Thought was just to use the value as is. When the ventilation guy wanted 40%, he just added 4000 to the value in the mosaic. But dont seem to want higher than 100.
Then a script is the way to go then.
Hm. Did you set the min/max values correctly?
(30.09.2019, 10:47)Daniel. Wrote: Hm. Did you set the min/max values correctly?
Default 0-100, fixed it. Testet from mosaic sending 3400 receiving 34% on the bus.
For now this will work. One beautiful day maybe i discover a script to convert. Or i will have a look in the Fb Editor.
Thanks for help..
1/1/1 is 4 byte floating point object, 1/1/2 is 2 byte unsigned object. Script has loop protection via event.sender check (se = script type event).
if event.sender ~= 'se' then
  grp.update('1/1/2', event.getvalue() * 100)
  grp.update('1/1/1', event.getvalue() / 100)
