Paradox EVO192 integration
The following scripts integrate Paradox EVO192 security panel. Paradox PRT3 printer module is used to connect the security panel to LM5 through RS232 serial port.
Thanks our forum member rebooter for contribution! Wink
guardZoneStatus library:
function guardzonefunction(zonenumber, zonestatus)
  guardZones = {
  [255255] = 'An empty zone has arrived',
  [01] = 'The main entrance. Motion Sensor.',
  [02] = 'The cabinet. Motion Sensor.',
  [03] = 'The garage. Motion Sensor.',
  [04] = 'The stairs. Motion Sensor.',
  [05] = 'The living room. Motion Sensor.',
  [06] = 'The dining room. Motion Sensor.',
  [07] = 'The kitchen. Motion Sensor.',
  [08] = 'Garage entrance. Motion Sensor.',
  [09] = 'The main entrance. Window Break Sensor ',
  [10] = 'The cabinet. Window Break Sensor ',
  [11] = 'The garage. Window Break Sensor ',
  [13] = 'Living room. Window Break Sensor ',
  [14] = 'Dining room. Window Break Sensor ',
  [15] = 'The kitchen. Window Break Sensor ',
  [16] = 'The garage door. Reed switch ',
  [17] = 'The main entrance. Reed switch ',
  [18] = 'Dining room. Curtain',
  [19] = 'Boiler room. Motion Sensor.',
  [20] = 'The boiler room. Window jammer
  [21] = 'Cinema hall. Motion Sensor',
  [22] = 'Pantry. Motion Sensor',
  [24] = 'SPA room. Motion Sensor',
  [25] = 'Children's 1. Motion sensor',
  [26] = 'Hall 2 floor. Motion Sensor.',
  [27] = 'Children's 2. Motion sensor',
  [28] = 'Master bedroom. Motion Sensor',
  [30] = 'Pajar basement',
  [31] = 'Fire 1st floor',
  [32] = 'Fire 2nd floor',
  [33] = 'Fire Sauna',
  [34] = 'Fire attic',
  [35] = 'Server fire',
  [36] = 'Under the stairs',
  [50] = 'House is armed',
  [51] = 'House is disarmed',
-- Arming with mast
  zonename = guardZones[zonenumber]
-- log ("Zone Nr triggered: "..zonenumber.." status: "..zonestatus.." "..zonename)
-- log(zonename)
-- log(zonestatus)
-- log(guardZones[zonenumber])
  if zonestatus == 'closed' then
    status = 1
  elseif zonestatus == 'opened' then
    status = 0
      if zonenumber == 1 then
            grp.update('8/0/1', status)
    elseif zonenumber == 2 then
--   zonename = guardZones[zonenumber]
          grp.update('8/0/2', status)
    elseif zonenumber == 3 then
          grp.update('8/0/3', status)
    elseif zonenumber == 4 then
          grp.update('8/0/4', status)
    elseif zonenumber == 5 then
          grp.update('8/0/5', status)
    elseif zonenumber == 6 then
          grp.update('8/0/6', status)
    elseif zonenumber == 7 then
          grp.update('8/0/7', status)
    elseif zonenumber == 8 then
          grp.update('8/0/8', status)
    elseif zonenumber == 9 then
          grp.update('8/0/9', status)
    elseif zonenumber == 10 then
          grp.update('8/0/10', status)
    elseif zonenumber == 11 then
          grp.update('8/0/11', status)
    elseif zonenumber == 13 then
          grp.update('8/0/13', status)
    elseif zonenumber == 14 then
          grp.update('8/0/14', status)
    elseif zonenumber == 15 then
          grp.update('8/0/15', status)
    elseif zonenumber == 16 then
          grp.update('8/0/16', status)
    elseif zonenumber == 17 then
          grp.update('8/0/17', status)
    elseif zonenumber == 18 then
          grp.update('8/0/18', status)
    elseif zonenumber == 19 then
          grp.update('8/0/19', status)
    elseif zonenumber == 20 then
          grp.update('8/0/20', status)
    elseif zonenumber == 21 then
          grp.update('8/0/21', status)
    elseif zonenumber == 22 then
          grp.update('8/0/22', status)
    elseif zonenumber == 24 then
          grp.update('8/0/24', status)
    elseif zonenumber == 25 then
          grp.update('8/0/25', status)
    elseif zonenumber == 26 then
          grp.update('8/0/26', status)
    elseif zonenumber == 27 then
          grp.update('8/0/27', status)
    elseif zonenumber == 28 then
          grp.update('8/0/28', status)
    elseif zonenumber == 30 then
          grp.update('8/0/30', status)
    elseif zonenumber == 31 then
          grp.update('8/0/31', status)
    elseif zonenumber == 32 then
          grp.update('8/0/32', status)
    elseif zonenumber == 33 then
          grp.update('8/0/33', status)
    elseif zonenumber == 34 then
          grp.update('8/0/34', status)
    elseif zonenumber == 35 then
          grp.update('8/0/35', status)
    elseif zonenumber == 36 then
          grp.update('8/0/36', status)
    -- process the status of security panel
    -- if armed then switch off lights in whole house
    elseif zonenumber == 50 then
    if grp.getvalue('0/5/8') == false then
      --    grp.update('0/5/5', status) --lights off
      grp.update('0/5/8', status) --security panel status
   elseif zonenumber == 51 then
     if grp.getvalue('0/5/8') then
    elseif zonenumber == 255255 then
    log("An empty zone has arrived")
    end --if zonenumber
RS232 communication script:
require('user.guardZoneStatus')
if not port then
  require('serial')
  port = serial.open('/dev/RS232', { baudrate = 9600, parity = 'none', databits = '8', stopbits = '1'})
  port:flush()
  line = ''
char = port:read(1, 1)
if char then
  if char == '\r' then
    line = line:trim()
    --log(line)
   -- mail('info@something.com', 'Installation X', line)
  --  loghex(line)
    zone = tonumber(string.sub(line,-2))
    if zone == nil  then
      zone = 255255
     -- log("An empty zone has arrived")
--   if (zone > 1) or (zone <37 ) then
    if (string.match(line,'opened')) == ('opened') then
      zoneStatus = 'opened'
      armstatus = grp.getvalue('0/5/8') --reading current status of security system
-- log(armstatus)
    if armstatus == true then
    grp.update('0/5/8', false) -- write those which are not armed
      zoneStatus = 'closed'
    end -- string.match
      -- parsing logs for setting to alarm
      if (string.match(line,'Arming')) == ('Arming') then
        zone = 50
    --  elseif (string.match(line,'  in')) == ('  in') then
    --    zoneStatus = 'closed'
    --    zone = 50
    elseif (string.match(line,'ode entere')) == ('ode entere') then
          zone = 51
    end -- string.match
      guardzonefunction(zone,zoneStatus)
  --  end -- test for zone nember 1 - 36
    line = ''
    line = line .. char
  end  -- if char '\r'
Hello!
Here is my updated communication script. Maybe this helps someone...
It allows to see zone status, get info about areas (if there is trouble in some area and if area is open or not), arm/disarm etc...
Also it polls every minute area status.
Residential script (EVO192 communication, sleep interval 0 seconds):
require('user.guardAreaStatus')
if not port then
  require('serial')
  port:flush()
  line = ''
control_house_security_ga = '10/1/0'                --area1 security status group address
control_woodstorage_security_ga = '10/1/1'    --area2 security status group address
security_code = '1234'
--log(char)
if char then
    line = line:trim()
    --log(line)
        event = string.sub(line,1,2)
   -- log(event)
    if event == 'G0' then
      eventnr = tonumber(string.sub(line,6,-5))
            area = tonumber(string.sub(line,10,-1))
      eventngr = tonumber(string.sub(line,2,4))
      if zone == nil  then
        zone = 255255
      guardzonefunction(eventngr,eventnr,area)
    elseif event == 'RA' then
      area = tonumber(string.sub(line,3,5))
      securitystatus_1 = string.sub(line,6,6)
      areastatus_1 = string.sub(line,7,7)
      areastatus_2 = string.sub(line,8,8)
      areastatus_3 = string.sub(line,9,9)
      areastatus_4 = string.sub(line,10,10)
      areastatus_5 = string.sub(line,11,11)
      areastatus_6 = string.sub(line,12,12)
      guardareafunction(area,securitystatus_1,areastatus_1,areastatus_2,areastatus_3,areastatus_4,areastatus_5,areastatus_6  )
    line = ''
    line = line .. char
  request = grp.getvalue('32/5/0')    --scheduled script changes object to true every minute. !!!ADD SCHEDULED SCRIPT!!!
  if request then
    port:write('RA001\r')                --send area1 status request command
    os.sleep(0.5)
    port:write('RA002\r')                --send area2 status request command
    grp.update('32/5/0', false)
  house_arm_disarm = grp.getvalue(control_house_security_ga)                        --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
  if house_arm_disarm == 1 then
    port:write('AA001A'..security_code..'\r')
    grp.update(control_house_security_ga, 0)
  elseif house_arm_disarm == 2 then
    port:write('AA001F'..security_code..'\r')
  elseif house_arm_disarm == 3 then
    port:write('AA001S'..security_code..'\r')
  elseif house_arm_disarm == 4 then
    port:write('AA001I'..security_code..'\r')
  elseif house_arm_disarm == 5 then
    port:write('AD001'..security_code..'\r')
  woodstorage_arm_disarm = grp.getvalue(control_woodstorage_security_ga)    --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
  if woodstorage_arm_disarm == 1 then
    port:write('AA002A'..security_code..'\r')
    grp.update(control_woodstorage_security_ga, 0)
  elseif woodstorage_arm_disarm == 2 then
    port:write('AA002F'..security_code..'\r')
  elseif woodstorage_arm_disarm == 3 then
    port:write('AA002S'..security_code..'\r')
  elseif woodstorage_arm_disarm == 4 then
    port:write('AA002I'..security_code..'\r')
  elseif woodstorage_arm_disarm == 5 then
    port:write('AD002'..security_code..'\r')
User library:
Script name: guardAreaStatus
function guardareafunction(areanumber, areastatus, areastatus1, areastatus2, areastatus3, areastatus4, areastatus5, areastatus6 ) --what must be process RA001DOONOOO; RA - Request area; 001 - Area number; D - Disarmed/Armed/Force armed/Stay armed/Instant armed; O - Zone in memory/Ok; O - Troube/Ok; N - Not ready/Ok; O - In programming/Ok; O - In alarm/Ok; O - Strobe/Ok
  house_area_status_ga = '10/0/0'
  woodstorage_area_status_ga = '10/0/1'
  house_area_trouble_ga = '10/3/0'
  woodstorage_area_trouble_ga = '10/3/1'
  house_area_not_ready_ga = '10/3/2'
  woodstorage_area_not_ready = '10/3/3'
  house_area_alarm_ga    = '10/2/0'
  woodstorage_area_alarm_ga = '10/2/1'
  if areastatus == 'D' then
    if areanumber == 1 then
      grp.write(house_area_status_ga, 0)
    elseif areanumber == 2 then
      grp.write(woodstorage_area_status_ga, 0)
  elseif areastatus == 'A' then
        grp.update(house_area_status_ga, 1)
      grp.update(woodstorage_area_status_ga, 1)
  elseif areastatus == 'F' then
        grp.update(house_area_status_ga, 2)
      grp.update(woodstorage_area_status_ga, 2)
  elseif areastatus == 'S' then
        grp.update(house_area_status_ga, 3)
      grp.update(woodstorage_area_status_ga, 3)
  elseif areastatus == 'I' then
        grp.update(house_area_status_ga, 4)
      grp.update(woodstorage_area_status_ga, 4)
  if areastatus2 == 'T' then
      grp.update(house_area_trouble_ga, true)
      grp.update(woodstorage_area_trouble_ga, true)
  elseif areastatus2 == 'O' then
      grp.update(house_area_trouble_ga, false)
      grp.update(woodstorage_area_trouble_ga, false)
  if areastatus3 == 'N' then
      grp.update(house_area_not_ready_ga, true)
      grp.update(woodstorage_area_not_ready, true)
  elseif areastatus3 == 'O' then
      grp.update(house_area_not_ready_ga, false)
      grp.update(woodstorage_area_not_ready, false)
  if areastatus5 == 'A' then
      grp.update(house_area_alarm_ga, true)
      grp.update(woodstorage_area_alarm_ga, true)
  elseif areastatus5 == 'O' then
      grp.update(house_area_alarm_ga, false)
      grp.update(woodstorage_area_alarm_ga, false)
Script name: guardZoneStatus
function guardzonefunction( eventgroup,eventnumber,areanumber)
  guardZones = {
  [01] = 'Tehnoruum PIR.',
  [02] = '1k Trepihall PIR.',
  [03] = 'Kontor PIR.',
  [04] = 'Esik PIR.',
  [05] = 'Elutuba PIR.',
  [06] = 'Magamistuba PIR.',
  [07] = 'Garderoob PIR.',
  [08] = 'Kuur PIR.',
  [09] = 'Mona PIR ',
  [10] = 'Cara PIR  ',
  [11] = '2k Trepihall PIR ',
  [12] = 'Tehnoruumi Suits ',
  [13] = '1 Trepihall Suit ',
  [14] = 'Kontori Suits ',
  [15] = 'Esiku Suits ',
  [16] = 'Elutoa Suits ',
  [17] = 'Magamistoa Suits ',
  [18] = 'Garderoob Suits',
  [19] = 'Mona Suits',
  [20] = 'Cara Suits',
  [21] = '2 Trepihall Suit',
  [22] = '2k Elutoa Suits',
  [23] = 'Kuuri Uks',
  [24] = 'Kontori Aken',
  [25] = 'Peauks',
  [26] = 'Köögi Aken.',
  [27] = 'Terrassi Uks',
  [28] = '1k Vannitoa Uks',
  [29] = '1k Vannitoa Aken',
  [30] = 'Magamistoa Aken',
  [31] = 'Kuuri Aken',
  [32] = 'Mona 1 Aken',
  [33] = 'Cara 1 Aken',
  [34] = '2k Vannitoa Aken',
  [35] = '2k Elutuba M',
  [36] = 'Mona 2 Aken',
  [37] = 'Cara 2 Aken',
  [38] = 'Valvekilp',
  house_area_exit_delay_ga = '10/0/2'
  house_area_entry_delay_ga = '10/0/3'
  woodstorage_area_exit_delay_ga = '10/0/4'
  woodstorage_area_entry_delay_ga = '10/0/5'
  if eventgroup == 0 or eventgroup == 1 then
    if eventgroup == 0 then
      grp.update('10/4/'..eventnumber, false)
    elseif eventgroup == 1 then
      grp.update('10/4/'..eventnumber, true)
  elseif eventgroup == 13 then
      grp.update(house_area_status_ga, 0)
      grp.update(woodstorage_area_status_ga, 0)
  elseif eventgroup == 64 then
    if eventnumber == 0 then
    elseif eventnumber == 1 then
    elseif eventnumber == 2 then
    elseif eventnumber == 3 then
    elseif eventnumber == 4 or eventnumber == 5 or eventnumber == 6 or eventnumber == 7 then
  elseif eventgroup == 65 then
        grp.update(house_area_exit_delay_ga, true)
        grp.update(woodstorage_area_exit_delay_ga, true)
        grp.update(house_area_entry_delay_ga, true)
        grp.update(woodstorage_area_entry_delay_ga, true)
    elseif eventnumber == 0 then
        grp.update(house_area_entry_delay_ga, false)
        grp.update(house_area_exit_delay_ga, false)
        grp.update(woodstorage_area_entry_delay_ga, false)
        grp.update(woodstorage_area_exit_delay_ga, false)
Resident script for communication check (EVO192 Communication check, sleep interval 10s):
last_timestamp = grp.find("10/0/0").updatetime --Area1 status (status is polled every minute from security system)
communication_error = grp.getvalue('10/3/4')
now = os.microtime()
if (now - last_timestamp) >= 120 then --if object hasn't updated on last 120s then generate communication error
  if communication_error == false then
    grp.update('10/3/4', true)
  if grp.getvalue('10/3/4')==true then
    grp.update('10/3/4', false)
Here is UI:
Another update to get integration done about 1 minute.
Now my script reads out all arealabels and zone labels (You don't need to know anything about EVO program). Also creates automatically group objects. I tested it couple days ago in my new project and really, integration takes about 1-2 minutes.  Cool
What you probably need to do is edit zone labels to more understandable form (paradox allows enter only 16 characters for area and zone name).
Program needs one main group address range (example 10/x/x)
Group address structure is like this:
security_main_ga = '10/' --'3-level' = main/middle/sub. Make sure that 10/0/0 - 10/7/X group addresses are not used. System creates objects automatically.
10/0/1 - Area 1 security status [0-DISARMED, 1-ARMED, 2-FORCE ARMED, 3-STAY ARMED, 4-INSTANT ARMED]
10/0/8 - Area 8 security status
10/0/11 - Area 1 exit delay
10/0/18 - Area 8 exit delay
10/0/21 - Area 1 entry delay
10/0/28 - Area 8 entry delay
10/0/31 - Area 1 alarm status
10/0/38 - Area 8 alarm status
10/0/41 - Area 1 trouble
10/0/48 - Area 8 trouble
10/0/51 - Area 1 not ready
10/0/58 - Area 8 not ready
10/1/1 - Area 1 control        [1-ARM, 2-FORCE ARM, 3-STAY ARM, 4-INSTANT ARM, 5-DISARM]
10/1/8 - Area 8 control
10/2/1 - Zone 1 status
10/2/xxx - Zone xxx status
All what you need to change is in resident script (group addresses).
Resident script (EVO192 communication, sleep interval 0):
require('user.guardAreaLabels')
require('user.guardZoneLabels')
command_enum = {
  [1] = 'A',
  [2] = 'F',
  [3] = 'S',
  [4] = 'I',
if not port then
  require('serial')
  port:flush()
  line = ''
request_area_status_ga = '32/5/0'  --Create scheduled script for this one. Write true every minute.
request_zone_labels_ga = '32/5/3'  --You need to change this to true only one time or if security zones are changed.
                                   --This also activates group address generation.
                                   --Make sure that zone label is not "Zone 001, Zone 002 etc because these zone names gonna be ignored.
request_area_labels_ga = '32/5/4'  --You need to change this to true only one time or if security areas are changed.
                                   --Make sure that area label is not "Area 001, Area 002 etc because these area names gonna be ignored.
request_zone_name_count = 50       --how many zones will be scanned to get zone labels.
active_areas = 1                   --How many areas are polled periodically. Starts on first area.
--log(char)
if char then
    line = line:trim()
    log(line)
   -- log(event)
      guardzonefunction(eventngr,eventnr,area,security_main_ga)
      guardareafunction(area,securitystatus_1,areastatus_1,areastatus_2,areastatus_3,areastatus_4,areastatus_5,areastatus_6,security_main_ga  )
    elseif event == 'AL' then
      name = string.sub(line,6,16)
      guardarealabelfunction(area, name,security_main_ga)
    elseif event == 'ZL' then
      zone = tonumber(string.sub(line,3,5))
      guardzonelabelfunction(zone, name,security_main_ga)
    line = ''
    line = line .. char
  request = grp.getvalue(request_area_status_ga)    --scheduled script changes object to true every minute
  if request then
    for i = 1, active_areas, 1 do
            port:write('RA00'.. i .. '\r')                --send area1 status request command
        os.sleep(0.2)
      if i==active_areas then
            grp.update(request_area_status_ga, false)
  request_area_names = grp.getvalue(request_area_labels_ga)
  if request_area_names then
    for i = 1, 8, 1 do
        port:write('AL00'..tostring(i)..'\r')
        os.sleep(0.2)
      grp.update(request_area_labels_ga, false)
  request_zone_names = grp.getvalue(request_zone_labels_ga)
  if request_zone_names then
    for i = 1, request_zone_name_count, 1 do
      if i<10 then
          port:write('ZL00'..tostring(i)..'\r')
          os.sleep(0.2)
        port:write('ZL0'..tostring(i)..'\r')
          os.sleep(0.2)
  grp.update(request_zone_labels_ga, false)
    exist = grp.alias(security_main_ga .. '1/' .. i)
      if exist ~= nil then
      AreaControl = grp.getvalue(security_main_ga .. '1/' .. i)     --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
      if AreaControl ~=0 then
        if AreaControl ~= 5 then
          port:write('AA00' .. i .. command_enum[AreaControl] .. security_code ..'\r')
          grp.update(security_main_ga .. '1/' .. i, 0)
          port:write('AD00' .. i .. security_code ..'\r')
User library (guardAreaLabels):
function guardarealabelfunction(areanumber, areaname, security_main_ga)
  if areaname ~= ('Area ' .. tonumber(areanumber)) then
    for i = 1, 7, 1 do
      if i==1 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber))
        if exist == nil then
          address = grp.create({
            datatype = dt.uint8,
            address = security_main_ga .. '0/' .. tonumber(areanumber),
              name = areaname .. ' security status',
            comment = 'Automatically created object - Security Area '.. tonumber(areanumber),
            units = '',
            tags = { },
      elseif i==2 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+10)
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+10,
              name = areaname .. ' exit delay',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' exit delay',
            units = '',
            tags = { },
      elseif i==3 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+20)
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+20,
              name = areaname .. ' entry delay',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' entry delay',
            units = '',
            tags = { },
      elseif i==4 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+30)
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+30,
              name = areaname .. ' alarm status',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' alarm status',
            units = '',
            tags = { },
      elseif i==5 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+40)
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+40,
              name = areaname .. ' trouble',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' trouble',
            units = '',
            tags = { },
      elseif i==6 then
        exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+50)
            datatype = dt.bool,
            address = security_main_ga .. '0/' .. tonumber(areanumber)+50,
              name = areaname .. ' not ready',
              comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' not ready',
            units = '',
            tags = { },
      elseif i==7 then
        exist = grp.alias(security_main_ga .. '1/' .. tonumber(areanumber))
            address = security_main_ga .. '1/' .. tonumber(areanumber),
              name = 'Control ' .. areaname,
              comment = 'Automatically created object - Control Security Area '.. tonumber(areanumber),
            units = '',
            tags = { },
User library (guardAreaStatus):
function guardareafunction(areanumber, areastatus, areastatus1, areastatus2, areastatus3, areastatus4, areastatus5, areastatus6, security_main_ga ) --what must be process RA001DOONOOO; RA - Request area; 001 - Area number; D - Disarmed/Armed/Force armed/Stay armed/Instant armed; O - Zone in memory/Ok; O - Troube/Ok; N - Not ready/Ok; O - In programming/Ok; O - In alarm/Ok; O - Strobe/Ok
    grp.write(security_main_ga .. '0/' .. areanumber , 0)
    grp.update(security_main_ga .. '0/' .. areanumber , 1)
    grp.update(security_main_ga .. '0/' .. areanumber , 2)
    grp.update(security_main_ga .. '0/' .. areanumber , 3)
    grp.update(security_main_ga .. '0/' .. areanumber , 4)
    grp.update(security_main_ga .. '0/' .. areanumber+40 , true)
    grp.update(security_main_ga .. '0/' .. areanumber+40 , false)
    grp.update(security_main_ga .. '0/' .. areanumber+50 , true)
    grp.update(security_main_ga .. '0/' .. areanumber+50 , false)
    grp.update(security_main_ga .. '0/' .. areanumber+30 , true)
    grp.update(security_main_ga .. '0/' .. areanumber+30 , false)
User library (guardZoneLabels):
function guardzonelabelfunction(zonenumber, zonename, security_main_ga)
  exist = grp.alias(security_main_ga .. '2/'.. tonumber(zonenumber))
    if zonenumber<10 then
      if zonename ~= ('Zone 00' .. tonumber(zonenumber)) then
          datatype = dt.bool,
          address = security_main_ga .. '2/'.. tonumber(zonenumber),
          name = zonename,
            comment = 'Automatically created object - Zone '.. tonumber(zonenumber),
          units = '',
          tags = { },
    elseif zonenumber>=10 and zonenumber<100 then
      if zonename ~= ('Zone 0' .. tonumber(zonenumber)) then
          datatype = dt.bool,
          name = zonename,
          units = '',
          tags = { },
    elseif zonenumber>=100 then
      if zonename ~= ('Zone ' .. tonumber(zonenumber)) then
          datatype = dt.bool,
          name = zonename,
          units = '',
          tags = { },
User library (guardZoneStatus):
function guardzonefunction( eventgroup,eventnumber,areanumber,security_main_ga)
      grp.update(security_main_ga .. '2/'..eventnumber, false)
      grp.update(security_main_ga .. '2/'..eventnumber, true)
  elseif eventgroup == 5 then -- disarm
    grp.update(security_main_ga .. '0/' .. areanumber , 0)
    grp.update(security_main_ga .. '0/' .. areanumber+10,false)         --reset exit delay
    grp.update(security_main_ga .. '0/' .. areanumber+20 , false)        --reset entry delay
  elseif eventgroup == 13 then -- disarm
  elseif eventgroup == 64 then --
        grp.write(security_main_ga .. '0/' .. areanumber , 1)
      grp.write(security_main_ga .. '0/' .. areanumber , 2)
      grp.write(security_main_ga .. '0/' .. areanumber , 3)
     grp.write(security_main_ga .. '0/' .. areanumber , 4)
      grp.update(security_main_ga .. '0/' .. areanumber+10 , true)
      grp.update(security_main_ga .. '0/' .. areanumber+20 , true)
      grp.update(security_main_ga .. '0/' .. areanumber+10 , false)
After you request area and zone names, give it some time to scan and create group objects. Mine needed about 15-20 seconds (1 area, 50 zones)...
All objects what are created automatically they have also object comment "Automatically created object - Security Area X", "Automatically created object - Zone XX" etc..
Hi, thank you for this script! I'm investigating the best possible way to integrate a security system with KNX in my next project. Satel has INT-KNX-2, which is great, but it has certain limitations (e.g. only 64 addresses). There are some pricey 3rd party modules for DSC. And there is Paradox with PRT3 and pricey 3rd party modules again, or using Logic Machine alternatively. The last option I like the most, because I'll probably put a Logic Machine into the project anyways.
Two questions:
1. Does this script work with the newer Paradox serial module? PRT3 is now discontinued and replaced.
2. Are zone changes reported imidiately? For example if a motion sensor detects motion, is this reported on the same second?
(01.12.2020, 21:05)mishoboss Wrote: Hi, thank you for this script! I'm investigating the best possible way to integrate a security system with KNX in my next project. Satel has INT-KNX-2, which is great, but it has certain limitations (e.g. only 64 addresses). There are some pricey 3rd party modules for DSC. And there is Paradox with PRT3 and pricey 3rd party modules again, or using Logic Machine alternatively. The last option I like the most, because I'll probably put a Logic Machine into the project anyways.
Two questions:
Hi!
I definitelly should choose LM to integrate security system. You have no limits when using LM. Can program whatever you want.
Answers:
1. I havent tested it but if all commands are the same then it will work.
2. Yes, this is realtime info. In one project I am using movement from security as triger and switch lights when brightness is below setpoint.
Hi, is there a way to control Paradox PGMs (outputs)?
(26.06.2021, 05:27)mishoboss Wrote: Hi, is there a way to control Paradox PGMs (outputs)?
I didn't find any straight solution because there is no command to control PGM output directly. PGM output is meant to control via some statements inside paradox.
But, this solution should work (haven't tested it by myself) but paradox uses this solution with RF remotes.
You can try to use utility key and create this kind of configuration (picture 1 attached). I think there is possible to create similar configuration in BabyWare also.
In LM add this code in residential script to test it out:
  utility_key1_grp_addr = 'x/x/x' -- turn PGM on group address
  utility_key2_grp_addr = 'x/x/x' -- turn PGM off group address
  utility_key1 = grp.getvalue(utility_key1_grp_addr) -- PGM on
  utility_key2 = grp.getvalue(utility_key2_grp_addr) -- PGM off
  if utility_key1==true or utility_key1==1 then
     port:write('UK001\r')
     grp.update(utility_key1_grp_addr, false)
     os.sleep(0.2)
  elseif utility_key2==true or utility_key2==1 then
     port:write('UK002\r')
     grp.update(utility_key2_grp_addr, false)
     os.sleep(0.2)
enable log(event) in residential script to see if command is accepted.
Unfortunately there is no request/status command to see what is PGM state.
Hope this helps.
Hello. Everything is perfect but I see that the connection is through RS-232 port. My initial question is if there is some possibility to manage a alarm central through http connection. This kind of central usually include web server.
Thank you.
Hi!
Thanks for your work, @fleeceable! If I can make this work it would save me a lot of work Smile
For now I'm receiving only nill and a <?> character as you can see in the attachment.
I think the problem may be in the PTR3 options. Can you please give me some pointers how to solve this?
André Neves
Check the baudrate settings. All examples here use 9600, but your device is set to 19200.
(22.02.2022, 12:09)admin Wrote: Check the baudrate settings. All examples here use 9600, but your device is set to 19200.
It is at 9600. I just made the print after a test at 19200.
ASCII protocol should only contain printable characters. Since you are getting <?> (unprintable character) it means that there's something wrong on the communication level.
You can also try to switch Tx and Rx cables on logic side.
Another way to test that your PRT3 module (and paradox program) works is to use RS232 to USB converter and connect PRT3 to computer. Then use Docklight (https://docklight.de/) program. If all settings are correct you should see some data on Docklight terminal...
I have used that Logic library on 4 sites and all works great.
(11.03.2022, 11:51)fleeceable Wrote: You can also try to switch Tx and Rx cables on logic side.
Problem solved!
It was a bad wire connection inside the DB9 connector. The gnd wire was disconected.
This library is great and helped a lot. THanks.
(18.07.2020, 14:37)fleeceable Wrote: ..
Nice work! Thanks...
Unfortunatelly PRP3 ASCII Protocol missing a way to bypass zones Sad
It is hard to understand why Paradox did not include Bypass function on the PRT3.
They have it with the IP module... Everyone should send an update request to Paradox to have it added to the PRT3. It takes numbers to get results.
