This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Daikin EKFCMBCB7 Modbus
#1
Hi,

Anyone successfully connected to a Daikin Modbus board (EKFCMBCB7)?

The modbus register list I got doesn't look like the correct one (the returning values are sketchy), but the D3 variation is not working at all.

I'm attaching the files the installer provided to me.

Thanks

Attached Files
.pdf   BMSmodbus EKFCMBCB full-2.pdf (Size: 4.8 MB / Downloads: 32)
.pdf   IM_EKFCMBCB7_tcm135-204242.PDF (Size: 1.05 MB / Downloads: 19)
Reply
#2
To get real input register address subtract 30001 from the documented address, for holding registers subtract 40001.
Reply
#3
(14.11.2023, 12:18)admin Wrote: To get real input register address subtract 30001 from the documented address, for holding registers subtract 40001.

That's not an issue, I know that. In fact I don't trust the register list and the actual module are corresponding to each other.
Reply
#4
I solved the issue - the installer didn't set somethings on the units.

I'm also attaching a json file for integration.

Attached Files
.json   daikin_EKFCMBCB7.json (Size: 13.82 KB / Downloads: 19)