EnOcean profile A5-20-01
We need to communicate and act on thermostatic valves EnOcean. The provider's documentation indicate to use the profile A5-20-01 but this one does'nt exists in the list. How can I do ? (signal kind : 0-100%)
Thank you for answer
Check this: https://forum.logicmachine.net/showthrea...61#pid4261
Based on Erwins lua-drivers I did an implementation of Thermokon SAB05 (https://www.thermokon.de/produkte/easyse...ren/sab05/) on a Wiser/SpaceLynk. I did some documentation too. But it's in German. Anyhow, if you are interested in this documentation I can dig it out and provide it in this forum.
Regards
(15.11.2019, 16:26)Erwin van der Zwart Wrote: Hi,
Thanks for sharing your link !! I will try integrate it soon.
I have little questions anyway :
--> I found a little error in the driver I think : line 100 / "update" at valve position feedback adress in the Active Harvesting Status section ??
--> Variables "Adress" (16/2/x) : has this section to be substituted according to the equipment (We have several valves...) or should we duplicate the lua driver for each equipment ??
--> Blocking problem : mapping EnOcean to KNX is impossible without a profile... which one can I choose in the list for complete working ?
Thank you again for sharing your experience !
JSK
This is a separate script not a profile. You need to use RAW profile in EnOcean tab. Script handles parsing of RAW value.
(21.11.2019, 07:50)admin Wrote: This is a separate script not a profile. You need to use RAW profile in EnOcean tab. Script handles parsing of RAW value.
It's all explained in the header of the script (:
Line 100 is not a error, this is not a update to the drive status value but a KNX value update command, i use grp.update on purpose as i don't see any reason to post feedback to the KNX bus, if you need it on KNX then you should change it to grp.write
Yes you need a seperate event based script for each drive, so if you have 10 drives you need 20x 4 byte objects and 10x event based scripts, each event script is attached to the Enocean incomming 4 byte RAW value, and you need to set 10x the response 4 byte object to Enocean Outgoing.  The addresses needs to be matched to the objects you create...