This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Send delta?
#3
I'm running version 20160116 (bottom left in the configurator) and the minimum is 1. Latest I've found here is from the end of 2015.

The 0.1 would be great for analog inputs too. That's where I need it the most. Generally speaking, the "standard" dead-zone is usually 0.5, but implemented only after the conversion.
Let's take the -35..+35C 0-10V sensor as example:
1C=0.1428V
In current situation "delta 1"=1V / 0.1428 = 7C
While if you implement the "delta 1" after the conversion it would be 0.1428V or 1C

br, Z