This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

DSE7320 Modbus help
#6
Mery Christmas,

Althought the profile and script works fine i get an "Read failed: Operation time out" on modbus error log.
I have tried with just 2 registers on profile but i still get the same error.

The slave (DSE7320) is configured at 19200mbps / 2 stop bits / Half duplex and master inactivity timeout 10s
The LM RTU settings for RS485 are as above and also on profile i have poll interval 30s and timeout 10s.

There are only two devices connected on the BUS LM and DSE7320 at ~30m distance. I also have fitted both ends with 120 ohm resistors and connected the ground on each other.

Cable is a multicore unshielded 4x0,16mm usualy used in alarm systems, could that be a problem?

DSE7320 min profile
Code:
{
"manufacturer": "Deep Sea Electronics",
"description": "DSE7320",
"mapping": [
  {"name": "Generator mode FB", "bus_datatype": "uint16", "type": "register", "address": 772, "datatype": "uint16"},
  {"name": "Generator engine battery voltage", "bus_datatype": "float16", "type": "register", "address": 1029, "datatype": "uint16", "value_multiplier": 0.1, "units":"V"}
]    
}
Reply


Messages In This Thread
DSE7320 Modbus help - by gtsamis - 18.12.2020, 12:51
RE: DSE7320 Modbus help - by admin - 18.12.2020, 12:59
RE: DSE7320 Modbus help - by gtsamis - 18.12.2020, 13:11
RE: DSE7320 Modbus help - by admin - 18.12.2020, 13:24
RE: DSE7320 Modbus help - by gtsamis - 21.12.2020, 08:35
RE: DSE7320 Modbus help - by gtsamis - 26.12.2020, 18:06
RE: DSE7320 Modbus help - by admin - 28.12.2020, 08:07
RE: DSE7320 Modbus help - by gtsamis - 28.12.2020, 08:16

Forum Jump: