Bacnet client app not fetching all bacnet devices
I am using LM5 KDC for knx -Bacnet ip integration for AC controlling. I installed Bacnet client app in LM5. After scanning it shows the 28 devices with their device ID. But when I scanned same bacnet bus by another software it shows that there are 30 devices.
2 devices are not shown by rescanning in Bacnet client app.I try to restart the Bacnet server but still not problem solved. If I try to delete the one of the  Bacnet device from client app then how to recover this deleted device
Can you try to install our backnet package and see if this will find all?
https://dl.openrb.com/lm-20-imx6/pkg/gen...8_imx6.ipk
System-System-Packages. You will have new tab in LM.
(11.02.2021, 08:37)Daniel. Wrote: Can you try to install our backnet package and see if this will find all?
During scanning it shows the error "cannot run scan while local BACnet server is running on the same port"
The BACnet devices which is not showing app that will now showing in BACnet tab
Please reply
You cant use bacnet server and client at the same time. You must disable it as it says.
(11.02.2021, 10:49)Daniel. Wrote: You cant use bacnet server and client at the same time. You must disable it as it says.
How it will be disable
Go to system, interface, bacnet and disable bacnet server.
(11.02.2021, 11:22)Daniel. Wrote: Go to system, interface, bacnet and disable bacnet server.
The ac which not showing in app now it showing in BACnet tab but how to link group address
After installing package still 2 BACnet devices are not appear in Bacnet client app
The bacnet client app is not designed to work on any bigger installation. You will most likely need to stick to script
https://openrb.com/logicmachine-as-bacnet-client/
Please reply
