This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Zigbee gateway integration
(25.04.2023, 17:50)CarlS Wrote:
(25.04.2023, 16:48)admin Wrote: Update the app to 20230425 and see if it helps.

Everything seems to be ok now

Thanks a lot Smile

Carl

It seems that there is a couple of problems with the device with profile name TuYa - 16A Relay / Smart Plug
(Manufacturer: _TZ3000_eyzb8yg3
Model: TS0121)

1. It does not report RmsCurrent, RmsVoltage and CurrentSummDelivered automatically, so I run this script every minute.
    I don't know if it should report automatically. However, the script works, and the group addresses are updated

Code:
zb = require('applibs.zigbee')

--Manual reading--

--Create table
local zbtable = {
    'CurrentSummDelivered'
}
zb.cmd('getnamedattributes', '943469fffe715fae',1794, zbtable,1)

--Create table
local zbtable2 = {
    'RmsVoltage',
    'RmsCurrent'
}

zb.cmd('getnamedattributes', '943469fffe715fae',2820, zbtable2,2)

2. When I write to the On/off group address the relay is turned on and off, but I get no response to the status group address.
Nothing is shown in the monitor.
Only this line in the log:
Code:
2023-04-26 17:07:32    ZB: sending ZCL message to 943469fffe715fae, cluster 0006:
{ FrameControl = [ "FrameTypeLocal", "DirectionToServer", "DisableDefaultResponse" ], TransactionSequenceNumber = 100, OnOffClusterFrame = { CommandIdentifier = "On" } }
Reply


Messages In This Thread
Zigbee gateway integration - by tigi - 26.04.2021, 14:28
RE: Zigbee gateway integration - by myg - 26.04.2021, 15:24
RE: Zigbee gateway integration - by Daniel - 26.04.2021, 15:38
RE: Zigbee gateway integration - by tigi - 26.04.2021, 16:00
RE: Zigbee gateway integration - by Daniel - 26.04.2021, 16:04
RE: Zigbee gateway integration - by tigi - 28.04.2021, 19:35
RE: Zigbee gateway integration - by admin - 29.04.2021, 07:36
RE: Zigbee gateway integration - by tigi - 05.05.2021, 12:47
RE: Zigbee gateway integration - by Daniel - 05.05.2021, 12:48
RE: Zigbee gateway integration - by tigi - 05.05.2021, 12:55
RE: Zigbee gateway integration - by Daniel - 05.05.2021, 13:01
RE: Zigbee gateway integration - by tigi - 05.05.2021, 15:50
RE: Zigbee gateway integration - by admin - 08.05.2021, 10:16
RE: Zigbee gateway integration - by tigi - 08.05.2021, 11:09
RE: Zigbee gateway integration - by clue9 - 13.05.2021, 14:35
RE: Zigbee gateway integration - by Daniel - 13.05.2021, 14:41
RE: Zigbee gateway integration - by clue9 - 15.05.2021, 14:23
RE: Zigbee gateway integration - by MLa - 14.05.2021, 21:05
RE: Zigbee gateway integration - by clue9 - 15.05.2021, 16:25
RE: Zigbee gateway integration - by admin - 17.05.2021, 07:12
RE: Zigbee gateway integration - by emme - 19.05.2021, 16:48
RE: Zigbee gateway integration - by Daniel - 20.05.2021, 08:31
RE: Zigbee gateway integration - by admin - 21.05.2021, 13:12
RE: Zigbee gateway integration - by tigi - 21.05.2021, 16:23
RE: Zigbee gateway integration - by admin - 24.05.2021, 09:45
RE: Zigbee gateway integration - by tigi - 28.05.2021, 17:10
RE: Zigbee gateway integration - by admin - 29.05.2021, 09:05
RE: Zigbee gateway integration - by tigi - 29.05.2021, 14:29
RE: Zigbee gateway integration - by admin - 01.06.2021, 11:26
RE: Zigbee gateway integration - by tigi - 01.06.2021, 22:54
RE: Zigbee gateway integration - by admin - 02.06.2021, 05:21
RE: Zigbee gateway integration - by tigi - 02.06.2021, 21:36
RE: Zigbee gateway integration - by clue9 - 18.06.2021, 23:52
RE: Zigbee gateway integration - by admin - 21.06.2021, 06:36
RE: Zigbee gateway integration - by clue9 - 23.06.2021, 16:47
RE: Zigbee gateway integration - by admin - 24.06.2021, 09:57
RE: Zigbee gateway integration - by tigi - 07.07.2021, 10:22
RE: Zigbee gateway integration - by admin - 07.07.2021, 11:50
RE: Zigbee gateway integration - by tigi - 07.07.2021, 12:29
RE: Zigbee gateway integration - by tigi - 16.07.2021, 07:47
RE: Zigbee gateway integration - by admin - 16.07.2021, 07:59
RE: Zigbee gateway integration - by tigi - 16.07.2021, 13:51
RE: Zigbee gateway integration - by tigi - 19.07.2021, 20:18
RE: Zigbee gateway integration - by admin - 20.07.2021, 13:09
RE: Zigbee gateway integration - by tigi - 20.07.2021, 16:18
RE: Zigbee gateway integration - by daniel.r - 21.07.2021, 12:12
RE: Zigbee gateway integration - by Daniel - 21.07.2021, 12:13
RE: Zigbee gateway integration - by tuxtof - 11.08.2021, 04:36
RE: Zigbee gateway integration - by Daniel - 11.08.2021, 07:50
RE: Zigbee gateway integration - by tigi - 04.01.2022, 17:50
RE: Zigbee gateway integration - by Bitver - 15.09.2021, 12:56
RE: Zigbee gateway integration - by admin - 16.09.2021, 10:37
RE: Zigbee gateway integration - by emme - 18.09.2021, 08:10
RE: Zigbee gateway integration - by admin - 20.09.2021, 10:56
RE: Zigbee gateway integration - by Bitver - 24.09.2021, 12:36
RE: Zigbee gateway integration - by admin - 24.09.2021, 12:41
RE: Zigbee gateway integration - by edos - 24.09.2021, 15:28
RE: Zigbee gateway integration - by admin - 27.09.2021, 06:20
RE: Zigbee gateway integration - by edos - 27.09.2021, 07:48
RE: Zigbee gateway integration - by admin - 27.09.2021, 07:49
RE: Zigbee gateway integration - by edos - 27.09.2021, 08:27
RE: Zigbee gateway integration - by admin - 01.10.2021, 09:57
RE: Zigbee gateway integration - by tomnord - 07.10.2021, 18:03
RE: Zigbee gateway integration - by admin - 04.10.2021, 06:24
RE: Zigbee gateway integration - by Daniel - 05.10.2021, 10:07
RE: Zigbee gateway integration - by Evens - 26.10.2021, 18:46
RE: Zigbee gateway integration - by admin - 27.10.2021, 06:35
RE: Zigbee gateway integration - by Evens - 27.10.2021, 15:25
RE: Zigbee gateway integration - by admin - 02.11.2021, 09:50
RE: Zigbee gateway integration - by Evens - 03.11.2021, 19:34
RE: Zigbee gateway integration - by Daniel - 03.11.2021, 22:25
RE: Zigbee gateway integration - by Evens - 04.11.2021, 18:01
RE: Zigbee gateway integration - by Daniel - 04.11.2021, 18:03
RE: Zigbee gateway integration - by Evens - 04.11.2021, 19:29
RE: Zigbee gateway integration - by gtsamis - 04.11.2021, 23:28
RE: Zigbee gateway integration - by admin - 05.11.2021, 07:22
RE: Zigbee gateway integration - by gtsamis - 05.11.2021, 09:23
RE: Zigbee gateway integration - by clue9 - 19.11.2021, 22:54
RE: Zigbee gateway integration - by admin - 23.11.2021, 08:33
RE: Zigbee gateway integration - by admin - 23.11.2021, 10:31
RE: Zigbee gateway integration - by hocine - 09.12.2021, 10:47
RE: Zigbee gateway integration - by admin - 09.12.2021, 12:01
RE: Zigbee gateway integration - by domonorte - 31.12.2021, 09:11
RE: Zigbee gateway integration - by admin - 02.01.2022, 13:03
RE: Zigbee gateway integration - by merel - 02.01.2022, 16:35
RE: Zigbee gateway integration - by domonorte - 03.01.2022, 06:31
RE: Zigbee gateway integration - by admin - 03.01.2022, 06:25
RE: Zigbee gateway integration - by admin - 03.01.2022, 06:32
RE: Zigbee gateway integration - by domonorte - 03.01.2022, 06:36
RE: Zigbee gateway integration - by admin - 03.01.2022, 06:41
RE: Zigbee gateway integration - by Daniel - 05.01.2022, 08:51
RE: Zigbee gateway integration - by merel - 07.01.2022, 22:32
RE: Zigbee gateway integration - by admin - 10.01.2022, 08:01
RE: Zigbee gateway integration - by merel - 16.01.2022, 09:06
RE: Zigbee gateway integration - by admin - 17.01.2022, 09:30
RE: Zigbee gateway integration - by AlexLV - 24.01.2022, 22:42
RE: Zigbee gateway integration - by AlexLV - 08.02.2022, 11:37
RE: Zigbee gateway integration - by admin - 08.02.2022, 14:26
RE: Zigbee gateway integration - by AlexLV - 09.02.2022, 11:25
RE: Zigbee gateway integration - by admin - 11.02.2022, 13:18
RE: Zigbee gateway integration - by MLa - 11.02.2022, 21:49
RE: Zigbee gateway integration - by GIA - 12.02.2022, 21:49
RE: Zigbee gateway integration - by clue9 - 15.02.2022, 22:29
RE: Zigbee gateway integration - by admin - 16.02.2022, 12:42
RE: Zigbee gateway integration - by GIA - 17.02.2022, 17:16
RE: Zigbee gateway integration - by GIA - 16.02.2022, 13:25
RE: Zigbee gateway integration - by admin - 16.02.2022, 13:34
RE: Zigbee gateway integration - by MLa - 16.02.2022, 14:46
RE: Zigbee gateway integration - by admin - 17.02.2022, 14:12
RE: Zigbee gateway integration - by MLa - 17.02.2022, 17:05
RE: Zigbee gateway integration - by Daniel - 17.02.2022, 17:14
RE: Zigbee gateway integration - by clue9 - 18.02.2022, 15:18
RE: Zigbee gateway integration - by clue9 - 03.04.2022, 19:44
RE: Zigbee gateway integration - by clue9 - 30.11.2022, 21:53
RE: Zigbee gateway integration - by admin - 05.04.2022, 11:11
RE: Zigbee gateway integration - by Bitver - 05.04.2022, 14:10
RE: Zigbee gateway integration - by stativko - 13.04.2022, 14:21
RE: Zigbee gateway integration - by admin - 14.04.2022, 12:44
RE: Zigbee gateway integration - by stativko - 18.04.2022, 11:24
RE: Zigbee gateway integration - by tigi - 19.04.2022, 11:02
RE: Zigbee gateway integration - by admin - 20.04.2022, 08:20
RE: Zigbee gateway integration - by Zen - 15.06.2022, 14:41
RE: Zigbee gateway integration - by tigi - 16.07.2022, 09:04
RE: Zigbee gateway integration - by Rune - 22.04.2022, 21:15
RE: Zigbee gateway integration - by admin - 25.04.2022, 14:19
RE: Zigbee gateway integration - by Zen - 29.04.2022, 15:49
RE: Zigbee gateway integration - by admin - 02.05.2022, 08:33
RE: Zigbee gateway integration - by tigi - 29.06.2022, 11:11
RE: Zigbee gateway integration - by admin - 29.06.2022, 12:05
RE: Zigbee gateway integration - by tigi - 30.06.2022, 11:06
RE: Zigbee gateway integration - by tigi - 14.07.2022, 10:39
RE: Zigbee gateway integration - by admin - 07.07.2022, 08:30
RE: Zigbee gateway integration - by admin - 08.07.2022, 05:24
RE: Zigbee gateway integration - by admin - 20.07.2022, 10:38
RE: Zigbee gateway integration - by Rune - 13.09.2022, 11:55
RE: Zigbee gateway integration - by admin - 13.09.2022, 12:03
RE: Zigbee gateway integration - by Daniel - 14.09.2022, 15:21
RE: Zigbee gateway integration - by Rune - 20.09.2022, 10:36
RE: Zigbee gateway integration - by admin - 20.09.2022, 10:48
RE: Zigbee gateway integration - by Zen - 04.10.2022, 13:57
RE: Zigbee gateway integration - by emme - 05.10.2022, 16:04
RE: Zigbee gateway integration - by admin - 06.10.2022, 13:47
RE: Zigbee gateway integration - by Zen - 07.10.2022, 14:40
RE: Zigbee gateway integration - by Kolargol - 17.10.2022, 20:08
RE: Zigbee gateway integration - by admin - 18.10.2022, 05:52
RE: Zigbee gateway integration - by Rune - 23.10.2022, 15:26
RE: Zigbee gateway integration - by admin - 24.10.2022, 08:26
RE: Zigbee gateway integration - by Rune - 24.10.2022, 10:20
RE: Zigbee gateway integration - by admin - 25.10.2022, 10:12
RE: Zigbee gateway integration - by jmir - 30.10.2022, 17:14
RE: Zigbee gateway integration - by admin - 31.10.2022, 06:47
RE: Zigbee gateway integration - by admin - 03.11.2022, 07:37
RE: Zigbee gateway integration - by clue9 - 06.11.2022, 22:48
RE: Zigbee gateway integration - by Daniel - 07.11.2022, 09:24
RE: Zigbee gateway integration - by clue9 - 07.11.2022, 13:47
RE: Zigbee gateway integration - by Daniel - 07.11.2022, 15:35
RE: Zigbee gateway integration - by tigi - 17.11.2022, 18:09
RE: Zigbee gateway integration - by Daniel - 18.11.2022, 08:53
RE: Zigbee gateway integration - by admin - 14.11.2022, 06:54
RE: Zigbee gateway integration - by watamat - 15.11.2022, 20:54
RE: Zigbee gateway integration - by CarlS - 19.11.2022, 12:15
RE: Zigbee gateway integration - by admin - 21.11.2022, 08:19
RE: Zigbee gateway integration - by CarlS - 21.11.2022, 09:11
RE: Zigbee gateway integration - by tigi - 28.11.2022, 15:29
RE: Zigbee gateway integration - by admin - 29.11.2022, 07:57
RE: Zigbee gateway integration - by admin - 01.12.2022, 07:13
RE: Zigbee gateway integration - by clue9 - 03.12.2022, 19:13
RE: Zigbee gateway integration - by Daniel - 05.12.2022, 09:06
RE: Zigbee gateway integration - by admin - 05.12.2022, 13:47
RE: Zigbee gateway integration - by clue9 - 05.12.2022, 16:28
RE: Zigbee gateway integration - by Rune - 09.12.2022, 21:45
RE: Zigbee gateway integration - by admin - 12.12.2022, 07:11
RE: Zigbee gateway integration - by Rune - 13.12.2022, 21:49
RE: Zigbee gateway integration - by admin - 14.12.2022, 08:41
RE: Zigbee gateway integration - by Rune - 15.12.2022, 11:00
RE: Zigbee gateway integration - by Daniel - 15.12.2022, 11:05
RE: Zigbee gateway integration - by stativko - 18.12.2022, 16:27
RE: Zigbee gateway integration - by admin - 19.12.2022, 11:00
RE: Zigbee gateway integration - by Rune - 27.12.2022, 12:35
RE: Zigbee gateway integration - by admin - 27.12.2022, 12:39
RE: Zigbee gateway integration - by Rune - 27.12.2022, 12:51
RE: Zigbee gateway integration - by admin - 27.12.2022, 12:59
RE: Zigbee gateway integration - by Rune - 27.12.2022, 13:11
RE: Zigbee gateway integration - by admin - 27.12.2022, 13:30
RE: Zigbee gateway integration - by Rune - 27.12.2022, 13:59
RE: Zigbee gateway integration - by emme - 02.01.2023, 14:25
RE: Zigbee gateway integration - by admin - 03.01.2023, 09:41
RE: Zigbee gateway integration - by admin - 09.01.2023, 08:45
RE: Zigbee gateway integration - by Zen - 25.01.2023, 17:54
RE: Zigbee gateway integration - by CarlS - 25.01.2023, 19:49
RE: Zigbee gateway integration - by tomnord - 25.01.2023, 21:07
RE: Zigbee gateway integration - by CarlS - 26.01.2023, 05:57
RE: Zigbee gateway integration - by tomnord - 26.01.2023, 08:42
RE: Zigbee gateway integration - by admin - 26.01.2023, 10:50
RE: Zigbee gateway integration - by Zen - 26.01.2023, 12:12
RE: Zigbee gateway integration - by Zen - 02.02.2023, 10:46
RE: Zigbee gateway integration - by admin - 01.02.2023, 08:25
RE: Zigbee gateway integration - by admin - 02.02.2023, 11:00
RE: Zigbee gateway integration - by Daniel - 02.02.2023, 11:04
RE: Zigbee gateway integration - by Zen - 02.02.2023, 13:58
RE: Zigbee gateway integration - by Zen - 07.02.2023, 17:27
RE: Zigbee gateway integration - by admin - 08.02.2023, 08:46
RE: Zigbee gateway integration - by Zen - 08.02.2023, 16:59
RE: Zigbee gateway integration - by Zen - 13.02.2023, 11:43
RE: Zigbee gateway integration - by admin - 13.02.2023, 11:45
RE: Zigbee gateway integration - by Zen - 15.02.2023, 15:01
RE: Zigbee gateway integration - by Daniel - 15.02.2023, 15:13
RE: Zigbee gateway integration - by MLa - 17.02.2023, 18:38
RE: Zigbee gateway integration - by admin - 22.02.2023, 13:57
RE: Zigbee gateway integration - by jmir - 23.02.2023, 08:05
RE: Zigbee gateway integration - by admin - 23.02.2023, 08:22
RE: Zigbee gateway integration - by jmir - 23.02.2023, 09:32
RE: Zigbee gateway integration - by admin - 23.02.2023, 09:34
RE: Zigbee gateway integration - by jmir - 23.02.2023, 10:11
RE: Zigbee gateway integration - by MLa - 23.02.2023, 19:55
RE: Zigbee gateway integration - by MLa - 25.02.2023, 16:51
RE: Zigbee gateway integration - by Daniel - 27.02.2023, 08:38
RE: Zigbee gateway integration - by MLa - 28.02.2023, 14:59
RE: Zigbee gateway integration - by Daniel - 28.02.2023, 15:16
RE: Zigbee gateway integration - by MLa - 28.02.2023, 16:26
RE: Zigbee gateway integration - by MLa - 02.03.2023, 17:17
RE: Zigbee gateway integration - by tigi - 28.02.2023, 22:45
RE: Zigbee gateway integration - by tigi - 02.03.2023, 11:45
RE: Zigbee gateway integration - by admin - 02.03.2023, 11:47
RE: Zigbee gateway integration - by tigi - 02.03.2023, 18:32
RE: Zigbee gateway integration - by tigi - 05.03.2023, 18:35
RE: Zigbee gateway integration - by Daniel - 06.03.2023, 08:43
RE: Zigbee gateway integration - by admin - 06.03.2023, 08:44
RE: Zigbee gateway integration - by tigi - 06.03.2023, 18:29
RE: Zigbee gateway integration - by jeeone - 11.04.2023, 07:17
RE: Zigbee gateway integration - by admin - 11.04.2023, 07:32
RE: Zigbee gateway integration - by jeeone - 11.04.2023, 08:06
RE: Zigbee gateway integration - by jeeone - 11.04.2023, 15:02
RE: Zigbee gateway integration - by Zen - 13.04.2023, 15:27
RE: Zigbee gateway integration - by Zen - 29.06.2023, 06:52
RE: Zigbee gateway integration - by admin - 25.04.2023, 11:01
RE: Zigbee gateway integration - by CarlS - 25.04.2023, 16:42
RE: Zigbee gateway integration - by admin - 25.04.2023, 16:48
RE: Zigbee gateway integration - by CarlS - 25.04.2023, 17:50
RE: Zigbee gateway integration - by CarlS - 26.04.2023, 15:45
RE: Zigbee gateway integration - by admin - 27.04.2023, 11:01
RE: Zigbee gateway integration - by CarlS - 27.04.2023, 11:39
RE: Zigbee gateway integration - by emme - 29.04.2023, 08:00
RE: Zigbee gateway integration - by MLa - 23.05.2023, 18:09
RE: Zigbee gateway integration - by admin - 24.05.2023, 07:52
RE: Zigbee gateway integration - by MLa - 24.05.2023, 17:35
RE: Zigbee gateway integration - by ikhy - 24.05.2023, 08:20
RE: Zigbee gateway integration - by admin - 24.05.2023, 08:33
RE: Zigbee gateway integration - by ikhy - 24.05.2023, 09:01
RE: Zigbee gateway integration - by admin - 25.05.2023, 07:09
RE: Zigbee gateway integration - by MLa - 03.06.2023, 08:15
RE: Zigbee gateway integration - by Rune - 31.05.2023, 19:34
RE: Zigbee gateway integration - by AISystem - 01.06.2023, 14:42
RE: Zigbee gateway integration - by admin - 01.06.2023, 17:04
RE: Zigbee gateway integration - by AISystem - 02.06.2023, 06:07
RE: Zigbee gateway integration - by admin - 02.06.2023, 06:13
RE: Zigbee gateway integration - by AISystem - 02.06.2023, 06:52
RE: Zigbee gateway integration - by admin - 02.06.2023, 07:10
RE: Zigbee gateway integration - by AISystem - 02.06.2023, 07:24
RE: Zigbee gateway integration - by admin - 02.06.2023, 07:47
RE: Zigbee gateway integration - by admin - 05.06.2023, 06:20
RE: Zigbee gateway integration - by MLa - 05.06.2023, 19:23
RE: Zigbee gateway integration - by Daniel - 06.06.2023, 08:29
RE: Zigbee gateway integration - by ikhy - 06.06.2023, 08:15
RE: Zigbee gateway integration - by AISystem - 07.06.2023, 05:22
RE: Zigbee gateway integration - by admin - 07.06.2023, 05:23
RE: Zigbee gateway integration - by AISystem - 07.06.2023, 06:14
RE: Zigbee gateway integration - by admin - 08.06.2023, 07:34
RE: Zigbee gateway integration - by AISystem - 08.06.2023, 11:01
RE: Zigbee gateway integration - by ikhy - 08.06.2023, 18:39
RE: Zigbee gateway integration - by ikhy - 09.06.2023, 06:16
RE: Zigbee gateway integration - by Daniel - 09.06.2023, 07:38
RE: Zigbee gateway integration - by ikhy - 09.06.2023, 08:00
RE: Zigbee gateway integration - by Daniel - 09.06.2023, 08:03
RE: Zigbee gateway integration - by ikhy - 09.06.2023, 11:42
RE: Zigbee gateway integration - by ikhy - 12.06.2023, 09:09
RE: Zigbee gateway integration - by admin - 12.06.2023, 09:21
RE: Zigbee gateway integration - by Daniel - 12.06.2023, 14:34
RE: Zigbee gateway integration - by Daniel - 12.06.2023, 15:49
RE: Zigbee gateway integration - by admin - 13.06.2023, 07:34
RE: Zigbee gateway integration - by Daniel - 13.06.2023, 08:26
RE: Zigbee gateway integration - by admin - 13.06.2023, 08:30
RE: Zigbee gateway integration - by Nikita - 28.06.2023, 09:04
RE: Zigbee gateway integration - by admin - 28.06.2023, 12:20
RE: Zigbee gateway integration - by Nikita - 29.06.2023, 06:39
RE: Zigbee gateway integration - by admin - 29.06.2023, 07:07
RE: Zigbee gateway integration - by Zen - 05.07.2023, 10:04
RE: Zigbee gateway integration - by admin - 05.07.2023, 14:24
RE: Zigbee gateway integration - by Zen - 06.07.2023, 07:04
RE: Zigbee gateway integration - by Zen - 06.07.2023, 08:40
RE: Zigbee gateway integration - by cranz - 07.07.2023, 07:34
RE: Zigbee gateway integration - by Zen - 24.07.2023, 08:01
RE: Zigbee gateway integration - by Zen - 27.07.2023, 08:13
RE: Zigbee gateway integration - by Zen - 28.08.2023, 07:09
RE: Zigbee gateway integration - by Daniel - 02.08.2023, 09:53
RE: Zigbee gateway integration - by Daniel - 02.08.2023, 10:07
RE: Zigbee gateway integration - by Sral1987 - 03.08.2023, 15:33
RE: Zigbee gateway integration - by admin - 08.08.2023, 07:58
RE: Zigbee gateway integration - by jmir - 08.08.2023, 08:01
RE: Zigbee gateway integration - by Sral1987 - 09.08.2023, 12:41
RE: Zigbee gateway integration - by hocine - 14.08.2023, 14:15
RE: Zigbee gateway integration - by Daniel - 14.08.2023, 14:16
RE: Zigbee gateway integration - by hocine - 16.08.2023, 11:21
RE: Zigbee gateway integration - by admin - 28.08.2023, 07:19
RE: Zigbee gateway integration - by Zen - 30.08.2023, 07:23
RE: Zigbee gateway integration - by Sral1987 - 02.09.2023, 08:52
RE: Zigbee gateway integration - by Daniel - 04.09.2023, 07:35
RE: Zigbee gateway integration - by Sral1987 - 04.09.2023, 11:41
RE: Zigbee gateway integration - by admin - 04.09.2023, 11:45
RE: Zigbee gateway integration - by Sral1987 - 04.09.2023, 13:49
RE: Zigbee gateway integration - by MLa - 08.09.2023, 16:43
RE: Zigbee gateway integration - by admin - 11.09.2023, 09:17
RE: Zigbee gateway integration - by Zen - 12.09.2023, 14:45
RE: Zigbee gateway integration - by Sral1987 - 12.09.2023, 11:58
RE: Zigbee gateway integration - by admin - 13.09.2023, 12:09
RE: Zigbee gateway integration - by Zen - 13.09.2023, 13:58
RE: Zigbee gateway integration - by Zen - 17.10.2023, 09:19
RE: Zigbee gateway integration - by lamgia99 - 10.11.2023, 09:08
RE: Zigbee gateway integration - by admin - 13.09.2023, 14:09
RE: Zigbee gateway integration - by Zen - 14.09.2023, 09:50
RE: Zigbee gateway integration - by Sral1987 - 13.09.2023, 19:16
RE: Zigbee gateway integration - by jmir - 15.09.2023, 08:07
RE: Zigbee gateway integration - by admin - 15.09.2023, 08:39
RE: Zigbee gateway integration - by Sral1987 - 16.10.2023, 10:38
RE: Zigbee gateway integration - by Daniel - 16.10.2023, 10:39
RE: Zigbee gateway integration - by admin - 16.10.2023, 12:08
New RS-232 Zigbee gateway - by CarlS - 24.10.2023, 11:57
RE: Zigbee gateway integration - by Daniel - 24.10.2023, 12:00
RE: Zigbee gateway integration - by CarlS - 24.10.2023, 13:07
RE: Zigbee gateway integration - by admin - 24.10.2023, 13:08
RE: Zigbee gateway integration - by CarlS - 24.10.2023, 19:12
RE: Zigbee gateway integration - by admin - 02.11.2023, 10:31
RE: Zigbee gateway integration - by a455115 - 06.11.2023, 11:09
RE: Zigbee gateway integration - by admin - 06.11.2023, 11:26
RE: Zigbee gateway integration - by domotiqa - 07.11.2023, 17:03
RE: Zigbee gateway integration - by a455115 - 10.11.2023, 11:06
RE: Zigbee gateway integration - by admin - 10.11.2023, 11:18
RE: Zigbee gateway integration - by lamgia99 - 11.11.2023, 01:22
RE: Zigbee gateway integration - by domotiqa - 14.11.2023, 10:46
RE: Zigbee gateway integration - by admin - 13.11.2023, 08:12
RE: Zigbee gateway integration - by lamgia99 - 14.11.2023, 06:37
RE: Zigbee gateway integration - by lamgia99 - 16.11.2023, 01:24
RE: Zigbee gateway integration - by admin - 16.11.2023, 08:13
RE: Zigbee gateway integration - by lamgia99 - 16.11.2023, 08:26
RE: Zigbee gateway integration - by DGrandes - 17.11.2023, 14:55
RE: Zigbee gateway integration - by Daniel - 17.11.2023, 15:00
RE: Zigbee gateway integration - by DGrandes - 17.11.2023, 15:03
RE: Zigbee gateway integration - by Daniel - 17.11.2023, 15:06
RE: Zigbee gateway integration - by DGrandes - 17.11.2023, 15:23
RE: Zigbee gateway integration - by Zen - 22.11.2023, 08:38
RE: Zigbee gateway integration - by admin - 22.11.2023, 08:50
RE: Zigbee gateway integration - by Zen - 27.11.2023, 10:55
RE: Zigbee gateway integration - by tom77 - 28.11.2023, 10:53
RE: Zigbee gateway integration - by admin - 28.11.2023, 11:15
RE: Zigbee gateway integration - by Zen - 28.11.2023, 15:08
RE: Zigbee gateway integration - by domotiqa - 29.11.2023, 09:13
RE: Zigbee gateway integration - by admin - 29.11.2023, 12:03
RE: Zigbee gateway integration - by tigi - 08.12.2023, 10:24
RE: Zigbee gateway integration - by Daniel - 08.12.2023, 10:29
RE: Zigbee gateway integration - by tigi - 08.12.2023, 10:34
RE: Zigbee gateway integration - by tigi - 10.12.2023, 19:27
RE: Zigbee gateway integration - by tigi - 13.12.2023, 13:52
RE: Zigbee gateway integration - by admin - 13.12.2023, 13:52
RE: Zigbee gateway integration - by tigi - 13.12.2023, 14:13
RE: Zigbee gateway integration - by tomnord - 14.12.2023, 14:15
RE: Zigbee gateway integration - by admin - 14.12.2023, 14:52
RE: Zigbee gateway integration - by tomnord - 15.12.2023, 07:18
RE: Zigbee gateway integration - by admin - 15.12.2023, 08:11
RE: Zigbee gateway integration - by tomnord - 15.12.2023, 13:27
RE: Zigbee gateway integration - by admin - 15.12.2023, 13:30
RE: Zigbee gateway integration - by tomnord - 31.12.2023, 10:32
RE: Zigbee gateway integration - by admin - 02.01.2024, 10:17
RE: Zigbee gateway integration - by tomnord - 02.01.2024, 12:28
RE: Zigbee gateway integration - by admin - 02.01.2024, 12:31
RE: Zigbee gateway integration - by tomnord - 02.01.2024, 16:11
RE: Zigbee gateway integration - by Daniel - 02.01.2024, 16:30
RE: Zigbee gateway integration - by Sral1987 - 03.01.2024, 12:57
RE: Zigbee gateway integration - by admin - 03.01.2024, 14:04
RE: Zigbee gateway integration - by alexll - 03.01.2024, 16:40
RE: Zigbee gateway integration - by Sral1987 - 06.01.2024, 14:30
RE: Zigbee gateway integration - by tomnord - 18.01.2024, 20:33
RE: Zigbee gateway integration - by Daniel - 19.01.2024, 08:30
RE: Zigbee gateway integration - by tomnord - 19.01.2024, 09:35
RE: Zigbee gateway integration - by admin - 19.01.2024, 09:42
RE: Zigbee gateway integration - by tomnord - 19.01.2024, 09:57
RE: Zigbee gateway integration - by admin - 19.01.2024, 10:05
RE: Zigbee gateway integration - by tomnord - 19.01.2024, 10:49
RE: Zigbee gateway integration - by tomnord - 20.01.2024, 09:53
RE: Zigbee gateway integration - by tomnord - 25.01.2024, 18:17
RE: Zigbee gateway integration - by Daniel - 26.01.2024, 08:28
RE: Zigbee gateway integration - by tomnord - 26.01.2024, 08:38
RE: Zigbee gateway integration - by Daniel - 26.01.2024, 08:40
RE: Zigbee gateway integration - by Zen - 29.01.2024, 15:10
RE: Zigbee gateway integration - by admin - 01.02.2024, 14:12
RE: Zigbee gateway integration - by admin - 13.02.2024, 08:03
RE: Zigbee gateway integration - by AlexandrT - 13.02.2024, 16:34
RE: Zigbee gateway integration - by Patrik - 13.02.2024, 20:50
RE: Zigbee gateway integration - by admin - 14.02.2024, 10:44
RE: Zigbee gateway integration - by AlexandrT - 14.02.2024, 15:00
RE: Zigbee gateway integration - by Rune - 16.02.2024, 12:03
RE: Zigbee gateway integration - by admin - 19.02.2024, 08:33
RE: Zigbee gateway integration - by AlexLV - 25.02.2024, 23:02
RE: Zigbee gateway integration - by Daniel - 26.02.2024, 08:55
RE: Zigbee gateway integration - by AlexLV - 26.02.2024, 15:17
RE: Zigbee gateway integration - by admin - 04.03.2024, 08:33
RE: Zigbee gateway integration - by admin - 04.03.2024, 09:25
RE: Zigbee gateway integration - by admin - 04.03.2024, 10:44
RE: Zigbee gateway integration - by busta - 29.03.2024, 12:57
RE: Zigbee gateway integration - by admin - 02.04.2024, 07:16
RE: Zigbee gateway integration - by alexll - 24.04.2024, 13:48
RE: Zigbee gateway integration - by busta - 25.04.2024, 17:17
RE: Zigbee gateway integration - by admin - 26.04.2024, 09:59
Zigbee gateway - by CristianAgata - 06.03.2022, 13:38
RE: Zigbee gateway - by admin - 07.03.2022, 07:40
RE: Zigbee gateway - by CristianAgata - 07.03.2022, 12:00
RE: Zigbee gateway - by admin - 07.03.2022, 12:07
RE: Zigbee gateway - by CristianAgata - 07.03.2022, 12:10
RE: Zigbee gateway - by CristianAgata - 13.03.2022, 11:37
RE: Zigbee gateway - by admin - 14.03.2022, 10:25
RE: Zigbee gateway - by CristianAgata - 14.03.2022, 11:06
RE: Zigbee gateway - by admin - 21.03.2022, 13:38
RE: Zigbee gateway - by emme - 02.04.2022, 08:48
RE: Zigbee gateway - by CristianAgata - 02.04.2022, 16:02
RE: Zigbee gateway - by clue9 - 03.04.2022, 19:11
RE: Zigbee gateway - by admin - 05.04.2022, 11:19
RE: Zigbee gateway - by gilles38 - 07.06.2022, 13:43
RE: Zigbee gateway - by admin - 10.06.2022, 09:45
RE: Zigbee gateway - by gilles38 - 13.06.2022, 10:59
RE: Zigbee gateway - by CarlS - 30.09.2022, 05:34
RE: Zigbee gateway - by CarlS - 18.10.2022, 06:24
RE: Zigbee gateway - by admin - 18.10.2022, 10:29
RE: Zigbee gateway - by watamat - 19.10.2022, 19:42
RE: Zigbee gateway - by admin - 20.10.2022, 06:20
RE: Zigbee gateway - by simone.muscat - 20.10.2022, 06:31
RE: Zigbee gateway - by watamat - 20.10.2022, 19:31
RE: Zigbee gateway - by watamat - 01.11.2022, 14:08
RE: Zigbee gateway - by watamat - 12.11.2022, 16:27

Forum Jump: