This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus RTU to TCP bridging
#11
yes, they skould be equiped with those. It goes some wiring inside the NSX breakers, and in the circuit diagram there's a circuit-breaker called Supply for NSX motors.

I've added a few more modbus registers to my profile, and I now try to read out the status registers 8020 and 8021.

I get the following response:
8020 = 905 ( command for close )
8021 = 775 ( error kode 7?, which means: Negative acknowledgment, The slave cannot perform the programming request sent by the master. )
Best regards
Christian