This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus: can't write on ALDES INSPIRAIR_TOP_B120
#1
Hi, 

I Create the attached modbus profile for the that Aldes module and I can't write on some register like the 257.

I asked their technical support and the answer was: 

"There is a particularity on Inspirair to write on a single register.


You need to select a length “2” to write on a single register.
For example to write on address 257 then you need to select register 256 with length 2 and write the value you need on address 257."



So how a have to modify the profile?

Thanks

Peppe

Attached Files
.json   INSPIRAIR_TOP_B120.json (Size: 1.63 KB / Downloads: 9)
Reply
#2
Add "datatype": "uint32"
------------------------------
Ctrl+F5
Reply
#3
ok, thank you!