BACnet Client and Server
Is it possible to change BACnet-port on the BACnet-client, and at the same time run BACnet-server on standard port?
Eirik
Are you using client app or scripts?
At the moment I'm testing the app.
Can easily change to script, as there is only a few datapoints I'm planning to read out from the device on port 47809(?) bac1.
Tried script, but got error on packages.
which package is the correct when using script?
For scripts you need the genohm-scada-bacnet package. There you can change port like this:
require('bacnet')
bacnet.port = 0xBAC1
bacnet.write(127001, 'binary value', 2305, true)
I don't see an option of changing the port in the BACnet client app.