This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus communication error via Mapper
#3
(20.09.2021, 15:33)admin Wrote: In read test you are using address 256 while in profile you have 40256. Try removing "40" part of the address in your profile.

Hi admin,

You were right.

However, it didn' t work right away.

Then, I tried removing fix Object mapping and I got readings.

Then I used profile with fix Object mapping and then it worked.

Do you have any idea why that might have happened?

Anyway, thanks for the help!

Hi,

Sorry to bother again but there is another case of this issue.

See frequency in attached files.

I attach the latest profile.

Thanks.

---

Finally, I found the solution. I had to change "Value send delta"...

In "Modbus profile description" we read:
"New value is sent when the difference between previously sent value and current value is larger than delta. Defaults to unset, send on any value changed"

Why did I had to change value?

I use a "automatic" way to create profiles. What should be the value of "value_delta" field to be set to default, that is to be send on any value change?

Thanks in advance!