This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

ocpp and knx homelynk
#1
I have a charge point  that works with ocpp. I wanna connect it to my homelynk and operated with knx but i don't know how to connect it .
Any idea?
Reply
#2
Do you have a SE charger? If yes you could use Modbus IP in the scenario.. I haven't seen any direct implementation of the open charge point protocol until now but with our chargers we use Modbus for local status and control and use OCPP only to connect the device to a public enabled platform.
Reply
#3
Hello Erwin,

I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible?

Thank you for your help
Reply
#4
(11.10.2021, 22:52)Erwin van der Zwart Wrote: Do you have a SE charger? If yes you could use Modbus IP in the scenario.. I haven't seen any direct implementation of the open charge point protocol until now but with our chargers we use Modbus for local status and control and use OCPP only to connect the device to a public enabled platform.

No, I cant use Modbus, that's my problem.
Reply
#5
(12.10.2021, 07:38)Kilogica Wrote: Hello Erwin,

I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible?

Thank you for your help

Yes it should have modbus as i already integrated this one on a project.. I disabled the not needed registers but kept them in the script

Code:
require('luamodbus')
mb = luamodbus.tcp()

-- Read Socket 1
mb:open('192.168.1.200', 502)
mb:connect()
mb:setslave(255)
--s1AL1 = mb:readregistervalue(350, 'float32', 'w') -- Current Phase 1
--s1AL2 = mb:readregistervalue(352, 'float32', 'w')
--s1AL3 = mb:readregistervalue(354, 'float32', 'w')
s1ET = mb:readregistervalue(356, 'uint32', 'w') -- Energy Total
--s1PT = mb:readregistervalue(358, 'float32', 'w') -- Current Power
--s1VL1L2 = mb:readregistervalue(360, 'float32', 'w') -- Voltage Phase 1 - Phase 2
--s1VL2L3 = mb:readregistervalue(362, 'float32', 'w')
--s1VL3L1 = mb:readregistervalue(364, 'float32', 'w')
--s1VL1N = mb:readregistervalue(366, 'float32', 'w') -- Voltage Phase 1 - Neutral
--s1VL2N = mb:readregistervalue(368, 'float32', 'w')
--s1VL3N = mb:readregistervalue(370, 'float32', 'w')
--log(s1AL1,s1AL2,s1AL3,s1ET,s1PT,s1VL1L2,s1VL2L3,s1VL3L1,s1VL1N,s1VL2N,s1VlLN)
mb:close()

-- Read Socket 2
mb:open('192.168.1.201', 502)
mb:connect()
mb:setslave(255)
--s2AL1 = mb:readregistervalue(350, 'float32', 'w')
--s2AL2 = mb:readregistervalue(352, 'float32', 'w')
--s2AL3 = mb:readregistervalue(354, 'float32', 'w')
s2ET = mb:readregistervalue(356, 'uint32', 'w')
--s2PT = mb:readregistervalue(358, 'float32', 'w')
--s2VL1L2 = mb:readregistervalue(360, 'float32', 'w')
--s2VL2L3 = mb:readregistervalue(362, 'float32', 'w')
--s2VL3L1 = mb:readregistervalue(364, 'float32', 'w')
--s2VL1N = mb:readregistervalue(366, 'float32', 'w')
--s2VL2N = mb:readregistervalue(368, 'float32', 'w')
--s2VL3N = mb:readregistervalue(370, 'float32', 'w')
--log(s2AL1,s2AL2,s2AL3,s2ET,s2PT,s2VL1L2,s2VL2L3,s2VL3L1,s2VL1N,s2VL2N,s2VL3N)
mb:close()

-- Sum Socket 1 and Socket 2
tET = s1ET + s2ET -- Sum energy total of socket 1 and 2
tETrounded = math.round(tET/1000,0) -- Total S + S2 from Wh to kWh

s1ET = math.round(s1ET/1000,0) -- Socket 1 from Wh to kWh
s2ET = math.round(s2ET/1000,0) -- Socket 2 from Wh to kWh

grp.checkupdate('4/1/22', s1ET) -- Update values
grp.checkupdate('4/1/23', s2ET)
grp.checkupdate('4/1/19', tETrounded)
Reply
#6
(13.10.2021, 18:21)Erwin van der Zwart Wrote:
(12.10.2021, 07:38)Kilogica Wrote: Hello Erwin,

I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible?

Thank you for your help

Yes it should have modbus as i already integrated this one on a project.. I disabled the not needed registers but kept them in the script

Code:
require('luamodbus')
mb = luamodbus.tcp()

-- Read Socket 1
mb:open('192.168.1.200', 502)
mb:connect()
mb:setslave(255)
--s1AL1 = mb:readregistervalue(350, 'float32', 'w') -- Current Phase 1
--s1AL2 = mb:readregistervalue(352, 'float32', 'w')
--s1AL3 = mb:readregistervalue(354, 'float32', 'w')
s1ET = mb:readregistervalue(356, 'uint32', 'w') -- Energy Total
--s1PT = mb:readregistervalue(358, 'float32', 'w') -- Current Power
--s1VL1L2 = mb:readregistervalue(360, 'float32', 'w') -- Voltage Phase 1 - Phase 2
--s1VL2L3 = mb:readregistervalue(362, 'float32', 'w')
--s1VL3L1 = mb:readregistervalue(364, 'float32', 'w')
--s1VL1N = mb:readregistervalue(366, 'float32', 'w') -- Voltage Phase 1 - Neutral
--s1VL2N = mb:readregistervalue(368, 'float32', 'w')
--s1VL3N = mb:readregistervalue(370, 'float32', 'w')
--log(s1AL1,s1AL2,s1AL3,s1ET,s1PT,s1VL1L2,s1VL2L3,s1VL3L1,s1VL1N,s1VL2N,s1VlLN)
mb:close()

-- Read Socket 2
mb:open('192.168.1.201', 502)
mb:connect()
mb:setslave(255)
--s2AL1 = mb:readregistervalue(350, 'float32', 'w')
--s2AL2 = mb:readregistervalue(352, 'float32', 'w')
--s2AL3 = mb:readregistervalue(354, 'float32', 'w')
s2ET = mb:readregistervalue(356, 'uint32', 'w')
--s2PT = mb:readregistervalue(358, 'float32', 'w')
--s2VL1L2 = mb:readregistervalue(360, 'float32', 'w')
--s2VL2L3 = mb:readregistervalue(362, 'float32', 'w')
--s2VL3L1 = mb:readregistervalue(364, 'float32', 'w')
--s2VL1N = mb:readregistervalue(366, 'float32', 'w')
--s2VL2N = mb:readregistervalue(368, 'float32', 'w')
--s2VL3N = mb:readregistervalue(370, 'float32', 'w')
--log(s2AL1,s2AL2,s2AL3,s2ET,s2PT,s2VL1L2,s2VL2L3,s2VL3L1,s2VL1N,s2VL2N,s2VL3N)
mb:close()

-- Sum Socket 1 and Socket 2
tET = s1ET + s2ET -- Sum energy total of socket 1 and 2
tETrounded = math.round(tET/1000,0) -- Total S + S2 from Wh to kWh

s1ET = math.round(s1ET/1000,0) -- Socket 1 from Wh to kWh
s2ET = math.round(s2ET/1000,0) -- Socket 2 from Wh to kWh

grp.checkupdate('4/1/22', s1ET) -- Update values
grp.checkupdate('4/1/23', s2ET)
grp.checkupdate('4/1/19', tETrounded)

Thank you! It Works!

I looked everywhere but I can't find anything in the documentation