Threads: 12
Hi, I have Mitsubishi Electric ME-200 device. it control all AC devices in my project. it connectedd to LM via Bacnet app
I have abot 50 AC units and need to map about 10 variables for each.
every map takes about 5 to 30 seconds after pressing "save"
is there a way to make mapping automatic? or make "save" procedure faster?
Threads: 6
I would never use 500 objects with the client, way to much…
The client is intended for limited amount of objects like a heatpump or some other device you need to add.
With your setup you should use a BMS as client and link it with BACnet server of the controller..
Threads: 37
I have a problem on customer Building.
I have setup communication with Air flow system Swegon with BAcnet Ip.
1/
My BIG PROBLEM is that when I try to map knx object to Bacnet Object, it's very long time to linked them (60sec). Then if I try to link a second one it doesn't work anymore. I saw that the SL reboot. So I try again and see that the Memory usage go very high, so it(s very painful to link other objetc, I need to wait, re-scan... and doesn't work everytime.
2/ Is there a place where I can download the app for offline site ? The customer didn't give Internet access to Spacelynk in this building
3/ In the Bacnet app view, is there a way to display the current value (add column).
I used to deal with:
https://openrb.com/logicmachine-as-bacnet-client/
I installed the ipk, but looks like I can't anymore and can't use require bacnet library
SE ECO EXPERT