problem with 4g modem
Hello
I asked for the 4g modem to be installed in the reactor, since a customer has only provided me with 4g sim, when the APN returns and the internet connects, I send the emails but I have an error in sending the SMS.
Does the SMS library also have to be modified in order to manage the new modem?
  below the error reported in the offending lines
function sendsms(number, message)
  require('socket')
  client = socket.udp()
  client:sendto(number .. ' ' .. message, '127.0.0.1', 12535)
This script has nothing to do with the SMS sending via modem it simply sends message to the resident script. Post your full resident SMS script and a screenshot from System config > Status > System status > Serial ports.
(31.01.2022, 15:30)admin Wrote: This script has nothing to do with the SMS sending via modem it simply sends message to the resident script. Post your full resident SMS script and a screenshot from System config > Status > System status > Serial ports.
resident sms
-- init
if not numbers then
  require('user.sms')
  require('json')
  require('socket')
  -- allowed numbers, SMS from other numbers will be ignored
  numbers = { '3332958126' }
  -- port number depends on modem model
  comport = 'ttyACM3'
  doreset = false -- set to true if USB reset is required before starting any communication
  -- if SIM PIN is enabled, uncomment the line below and replace 0000 with SIM PIN
  -- pincode = '0000'
  -- command parser
  parser = function(cmd, sender)
    local find, pos, name, mode, offset, value, dvalue, obj, message
    cmd = cmd:trim()
    mode = cmd:sub(1, 1):upper()
    -- invalid request
    if mode ~= 'W' and mode ~= 'R' then
      return
    cmd = cmd:sub(3):trim()
    -- parse object name/address
    find = cmd:sub(1, 1) == '"' and '"' or ' '
    offset = find == '"' and 1 or 0
    -- pad with space when in read mode
    if mode == 'R' and find == ' ' then
      cmd = cmd .. ' '
    -- find object name
    pos = cmd:find(find, 1 + offset, true)
    -- name end not found, stop
    if not pos then
      return
    -- get name part
    name = cmd:sub(1 + offset, pos - offset):trim()
    if mode == 'W' then
      value = cmd:sub(pos + offset):trim()
      if #value > 0 then
        -- try decoding value
        dvalue = json.pdecode(value)
        if dvalue ~= nil then
          value = dvalue
        -- send to bus
        grp.write(name, value)
    -- read request
      obj = grp.find(name)
      -- object not known
      if not obj then
        return
      -- send read request and wait for an update
      obj:read()
      os.sleep(1)
      -- read new value
      value = grp.getvalue(name)
      -- got no value
      if value == nil then
        return
      -- add object name if specified
      if obj.name then
        name = string.format('%s (%s)', obj.name, obj.address)
      message = string.format('Value of %s is %s', name, json.encode(value))
      modem:sendsms('+' .. sender, message)
  -- incoming sms handler
  handler = function(sms)
    --alert('incoming sms: [%s] %s', tostring(sms.sender), tostring(sms.data))
    -- sms from known number, call parser
    if table.contains(numbers, sms.sender) then
      --parser(sms.data, sms.sender)
  -- check local udp server for messages to send
  udphandler = function(server)
    -- check for local sms to send
    local msg = server:receive()
    -- got no message
    if not msg then
      return
    -- split into number and message
    local sep = msg:find(' ')
    if not sep then
      return
    --alert('sending sms: ' .. msg)
    modem:sendsms(msg:sub(1, sep - 1), msg:sub(sep + 1))
-- handle data from modem
if modem then
  if modem:run() then
    udphandler(server)
    --alert('SMS handler lost connection')
    modem:reinit()
-- modem init
  --alert('SMS handler init')
  -- open serial port
  modem = AT:init('/dev/' .. comport, doreset)
  -- init ok
  if modem then
    -- set sms handler
    modem:setsmshandler(handler)
    -- send pin if set
    if pincode then
      modem:send('AT+CPIN=' .. pincode)
      modem:read()
    -- set to pdu mode
    modem:send('AT+CMGF=0')
    -- enable sms notifications
    modem:send('AT+CNMI=1,1,0,0,0')
    -- fixup encoding
    modem:send('AT+CSCS="GSM"')
    -- delete all saved messages
    modem:send('AT+CMGD=1,4')
    -- local udp server for sending sms
    server = socket.udp()
    server:setsockname('127.0.0.1', 12535)
    server:settimeout(0.1)
    --alert('SMS handler started')
  -- init failed
    --alert('SMS USB init failed')
-- init
if not numbers then
  require('user.sms')
  require('json')
  require('socket')
  comport = 'ttyACM3'
  -- pincode = '0000'
  -- command parser
    cmd = cmd:trim()
    -- invalid request
      return
      cmd = cmd .. ' '
    -- find object name
    if not pos then
      return
    -- get name part
    if mode == 'W' then
      if #value > 0 then
          value = dvalue
        -- send to bus
    -- read request
      -- object not known
      if not obj then
        return
      obj:read()
      os.sleep(1)
      -- read new value
      -- got no value
        return
      if obj.name then
    -- got no message
    if not msg then
      return
    if not sep then
      return
if modem then
  if modem:run() then
    udphandler(server)
    modem:reinit()
-- modem init
  -- open serial port
  -- init ok
  if modem then
    -- set sms handler
    -- send pin if set
    if pincode then
      modem:read()
    -- set to pdu mode
    -- fixup encoding
  -- init failed
user library
AT = {
  -- 7-bit alphabet
  alphabet = {
    64, 163, 36, 165, 232, 233, 249, 236, 242, 199, 10, 216, 248,
    13, 197, 229, 10, 95, 10, 10, 10, 10, 10, 10, 10, 10, 10, 38,
    198, 230, 223, 201, 32, 33, 34, 35, 164, 37, 38, 39, 40, 41,
    42, 43, 44, 45, 46, 47, 48, 49, 50, 51, 52, 53, 54, 55, 56,
    57, 58, 59, 60, 61, 62, 63, 161, 65, 66, 67, 68, 69, 70, 71,
    72, 73, 74, 75, 76, 77, 78, 79, 80, 81, 82, 83, 84, 85, 86,
    87, 88, 89, 90, 196, 214, 209, 220, 167, 191, 97, 98, 99, 100,
    101, 102, 103,  104, 105, 106, 107, 108, 109, 110, 111, 112,
    113, 114, 115, 116, 117, 118, 119, 120, 121, 122, 228, 246,
    241, 252, 224
  parsepdu = function(pdu)
    local data, len, msg, data, sender, offset, ntype, timestamp
    msg = {}
    -- offset from service center number
    offset = tonumber(pdu:sub(1, 2), 16) * 2
    -- sender number length
    len = tonumber(pdu:sub(offset + 5, offset + 6), 16)
    len = math.ceil(len / 2) * 2
    -- sender number type
    ntype = tonumber(pdu:sub(offset + 7, offset + 8), 16)
    ntype = bit.band(bit.rshift(ntype, 4), 0x07)
    -- raw sender number
    sender = pdu:sub(offset + 9, offset + len + 8)
    -- decode sender number
    msg.sender = AT.decodesender(sender, ntype)
    -- timestamp --
    offset = offset + len + 13
    timestamp = pdu:sub(offset, offset + 13)
    timestamp = AT.decodeswapped(timestamp)
    msg.timestamp = AT.decodetime(timestamp)
    -- message
    len = tonumber(pdu:sub(offset + 14, offset + 15), 16)
    data = pdu:sub(offset + 16)
    msg.data = AT.decode7bit(data, len)
    return msg
  end,
  -- decode sender address depending on source type
  decodesender = function(sender, ntype)
    if ntype == 5 then
      return AT.decode7bit(sender)
      return AT.decodeswapped(sender)
  end,
  -- decode time in sms pdu
  decodetime = function(timestamp)
    local offset, year, time
    offset = tonumber(timestamp:sub(13, 14)) or 0
    offset = offset * 15 * 60
    year = tonumber(timestamp:sub(1, 2))
    time = os.time({
      year = year < 70 and (2000 + year) or (1900 + year),
      month = tonumber(timestamp:sub(3, 4)),
      day = tonumber(timestamp:sub(5, 6)),
      hour = tonumber(timestamp:sub(7, 8)),
      min = tonumber(timestamp:sub(9, 10)),
      sec = tonumber(timestamp:sub(11, 12))
    }) or os.time()
    return time
  end,
  -- convert swapped number to normal
  decodeswapped = function(data)
    local i, nr, len, buf
    buf = {}
    -- real byte length
    len = math.floor(data:len() / 2)
    -- read 2 bytes at once
    for i = 1, len do
      -- convert low byte to number
      nr = tonumber(data:sub(i * 2, i * 2))
      if nr then
        table.insert(buf, tostring(nr))
      -- convert high byte to number
      nr = tonumber(data:sub(i * 2 - 1, i * 2 - 1))
      if nr then
    return table.concat(buf)
  end,
  -- convert from 7 bit char to 8 bit
  from7bit = function(c)
    if c < 128 then
      return string.char(AT.alphabet[ c + 1 ])
      return ' '
  end,
  -- converts from 7 bit to 8 bit
  decode7bit = function(data, len)
    local i, o, byte, prev, curr, mask, buf, res
    -- convert to binary string
    data = lmcore.hextostr(data, true)
    -- init vars
    o = 0
    prev = 0
    buf = {}
    for i = 1, data:len() do
      byte = data:byte(i, i)
      -- get 7 bit data
      mask = bit.lshift(1, 7 - o) - 1
      -- get current chunk
      curr = bit.band(byte, mask)
      curr = bit.lshift(curr, o)
      curr = bit.bor(curr, prev)
      -- save bit chunk
      prev = bit.rshift(byte, 7 - o)
      -- add to buffer
      table.insert(buf, AT.from7bit(curr))
      -- every 7th step prev will have a full char
      if o == 6 then
        table.insert(buf, AT.from7bit(prev))
        prev = 0
      o = (o + 1) % 7
    -- catch last char in buffer
    if prev > 0 then
    -- flatten buffer
    res = table.concat(buf)
    if len then
      res = res:sub(1, len)
    return res
function AT:init(dev, reset)
  require('serial')
  local t = setmetatable({}, { __index = AT })
  t.dev = dev
  while true do
    if t:reinit(30, reset) then
      break
      if reset then
        t:reset()
        return nil
  return t
function AT:open(timeout)
  local port
  while true do
    if io.exists(self.dev) then
      port = serial.open(self.dev)
      if port then
        break
    if timeout then
      timeout = timeout - 1
      if timeout <= 0 then
        return false
    os.sleep(1)
  self.port = port
  self.buffer = {}
  return true
function AT:reset()
  --alert('modem reset')
  os.execute('usbreset /dev/bus/usb/001/001')
function AT:reinit(timeout, reset)
  local res
  if reset then
    self:reset()
  res = self:open(timeout)
  self.buffer = {}
  return res
function AT:close()
  if self.port then
    self.port:close()
    self.port = nil
-- read single line from port
function AT:read(timeout)
  local char, err, timeout, deftimeout, line
  -- default timeout is 1 second, converted to 0.1 sec ticks
  timeout = tonumber(timeout) or 1
  timeout = timeout * 10
  deftimeout = timeout
  -- read until got one line or timeout occured
  while timeout > 0 do
    -- read 1 char
    char, err = self.port:read(1, 0.1)
    -- got data
    if char then
      -- got LF, end of line
      if char == '\n' then
        -- convert to string and empty buffer
        line = table.concat(self.buffer)
        self.buffer = {}
        line = line:trim()
        -- return only lines with data
        if #line > 0 then
          return line
        -- reset timeout
          timeout = deftimeout
      -- ignore CR
      elseif char ~= '\r' then
        table.insert(self.buffer, char)
    -- read timeout
    elseif err == 'timeout' then
    -- other error
      break
  print('error', err)
  return nil, err
-- blocking read until cmd is received
function AT:readuntil(cmd, timeout)
  local line, err
  timeout = timeout or 5
    line, err = self:read()
    -- read line ok
    if line then
      if line == cmd or line == 'COMMAND NOT SUPPORT' or line:match('ERROR') then
        return line
        err = 'invalid line'
    -- timeout
    -- other error
      break
  return nil, err
-- send command to terminal
function AT:send(cmd)
  local res, err = self.port:write(cmd .. '\r\n')
  -- write ok, get local echo
  if res then
    res, err = self:readuntil(cmd)
    self:read()
  return res, err
-- main handler
function AT:run()
  local res, err, cmd, pos, sms
  res, err = self:read()
  if err then
    return err == 'timeout'
  -- check for incoming command
  if res:sub(1, 1) ~= '+' then
    return true
  pos = res:find(':', 1, true)
  if not pos then
    return true
  -- get command type
  cmd = res:sub(2, pos - 1)
  -- check only for incoming sms
  if cmd ~= 'CMTI' then
    return
  -- read from sim
  sms = self:incsms(res)
  -- sms seems to be valid, pass to handler if specified
  if sms and self.smshandler then
    self.smshandler(sms)
  return true
function AT:incsms(res)
  local chunks, index, sms
  -- get message index from result
  chunks = res:split(',')
  if #chunks == 2 then
    -- get index and read from it
    index = tonumber(chunks[ 2 ])
    sms = self:readsms(index)
    -- delete sms from store
    self:deletesms(index)
  return sms
-- delete sms at index
function AT:deletesms(index)
  local cmd, res
  -- send delete request
  cmd = 'AT+CMGD=' .. index
  res = self:send(cmd)
  return res
-- read sms at index
function AT:readsms(index)
  local cmd, res, sms
  cmd = 'AT+CMGR=' .. index
  -- no message at then index
  if res == 'OK' then
    return nil, 'not found'
  -- read sms pdu and try decoding
  sms = self:read()
  res, sms = pcall(AT.parsepdu, sms)
  -- decode failed
  if not res then
    return nil, sms
  -- wait for ok from modem
  self:readuntil('OK')
  return sms
function AT:sendsms(number, message)
  local cmd, res
  -- switch to text mode
  self:send('AT+CMGF=1')
  -- set number
  cmd = string.format('AT+CMGS="%s"', number)
  -- number seems to be valid
  if res ~= 'ERROR' then
    -- message and CTRL+Z
    self.port:write(message .. string.char(0x1A))
    res = self:readuntil('OK')
  -- switch back to pdu mode
  self:send('AT+CMGF=0')
  return res
-- set sms handler
function AT:setsmshandler(fn)
  if type(fn) == 'function' then
    self.smshandler = fn
table.contains = function(t, v)
  for _, i in pairs(t) do
    if i == v then
      return true
  require('socket')
Replace ttyACM3 with ttyUSB2
(01.02.2022, 08:20)admin Wrote: Replace ttyACM3 with ttyUSB2
Nothing
I have this error when i try send sms
User library sms:465: attempt to index global 'client' (a nil value)
stack traceback:
User library sms:465: in function 'sendsms'
but in other reactor works
thanks
Replace the whole sendsms function with this and check if it works. Also check if you have any messages in Logs.
  local client, err = require('socket').udp()
  if client then
    client:close()
    log('failed to created socket: ' .. tostring(err))
(01.02.2022, 12:18)admin Wrote: Replace the whole sendsms function with this and check if it works. Also check if you have any messages in Logs.
  if client then
    client:close()
nothinig in log but nothing sms send
You have the same code in the resident script twice, this can lead to errors. You've also commented out all alerts so there's no way of knowing if the script is working or not.
Replace your resident script with this and post what you get in alerts:
-- init
if not numbers then
  require('user.sms')
  require('json')
  require('socket')
  comport = 'ttyACM3'
  -- pincode = '0000'
  -- command parser
    cmd = cmd:trim()
    -- invalid request
      return
      cmd = cmd .. ' '
    -- find object name
    if not pos then
      return
    -- get name part
    if mode == 'W' then
      if #value > 0 then
          value = dvalue
        -- send to bus
    -- read request
      -- object not known
      if not obj then
        return
      obj:read()
      os.sleep(1)
      -- read new value
      -- got no value
        return
      if obj.name then
    -- got no message
    if not msg then
      return
    if not sep then
      return
if modem then
  if modem:run() then
    udphandler(server)
    modem:reinit()
-- modem init
  -- open serial port
  -- init ok
  if modem then
    -- set sms handler
    -- send pin if set
    if pincode then
      modem:read()
    -- set to pdu mode
    -- fixup encoding
  -- init failed
(01.02.2022, 13:35)admin Wrote: You have the same code in the resident script twice, this can lead to errors. You've also commented out all alerts so there's no way of knowing if the script is working or not.
-- init
if not numbers then
  require('user.sms')
  require('json')
  require('socket')
  comport = 'ttyACM3'
  -- pincode = '0000'
  -- command parser
    cmd = cmd:trim()
    -- invalid request
      return
      cmd = cmd .. ' '
    -- find object name
    if not pos then
      return
    -- get name part
    if mode == 'W' then
      if #value > 0 then
          value = dvalue
        -- send to bus
    -- read request
      -- object not known
      if not obj then
        return
      obj:read()
      os.sleep(1)
      -- read new value
      -- got no value
        return
      if obj.name then
    -- got no message
    if not msg then
      return
    if not sep then
      return
if modem then
  if modem:run() then
    udphandler(server)
    modem:reinit()
-- modem init
  -- open serial port
  -- init ok
  if modem then
    -- set sms handler
    -- send pin if set
    if pincode then
      modem:read()
    -- set to pdu mode
    -- fixup encoding
  -- init failed
problem to init
Sorry, that was an old script. Replace ttyACM3 with ttyUSB2 and restart the script via disable/enable.
(01.02.2022, 14:56)admin Wrote: Sorry, that was an old script. Replace ttyACM3 with ttyUSB2 and restart the script via disable/enable.
Same error , need som in init script ?
Can you provide remote access to your LM?
(02.02.2022, 09:13)admin Wrote: Can you provide remote access to your LM?
via zerotier is ok ?
Yes, send your network ID, LM ZeroTier IP and admin password via PM.
Check if it's working now. You had a space after the serial port name so it did not work:
comport = 'ttyUSB2 '
(02.02.2022, 09:53)admin Wrote: Check if it's working now. You had a space after the serial port name so it did not work:
tanks a lot
Hello
For the problem of sending sms I solved with your help in 2 reactor out of 3, in the third with the same scripts, if I text the sms calling send it works, while if it is called from the script the alalrme event does not work, while the mails from the same script do
The alalrme event scripts I checked it are like in the reactor it works in, I'm getting lost and I don't know where.
I accept advice
Thank you
Have you replaced the sendsms function as specified? https://forum.logicmachine.net/showthrea...1#pid24831
Do you have anything in alerts and logs?
(03.02.2022, 07:27)admin Wrote: Have you replaced the sendsms function as specified? https://forum.logicmachine.net/showthrea...1#pid24831
Hello
I found the problem, the phone number had a space at the end for which it was not valid, now I try how to remove the spaces before and after, both for the phone number and if I can also for the email address so as to no longer have the problem.
Thank you