Hi,
I have a Astra Pool heat pump and i would like some help on the profile.
Can i write multiple coils via the profile? What datatatype should i use on the object? e.g. coils 0x211 & 0x212
Thanks in advance
Posts: 8189
Threads: 43
Joined: Jun 2015
Reputation:
473
Using multiple coils like this is not supported. You can use register with bitmask instead.
Posts: 187
Threads: 43
Joined: Jul 2015
Reputation:
2
(21.03.2022, 12:27) admin Wrote: Using multiple coils like this is not supported. You can use register with bitmask instead.
Would that work?
{ "name": "Heat Pump Mode bit1", "address": 33, "bus_datatype": "bool", "datatype":"uint16", "type": "register", "value_bitmask":0x2, "write_bitmask": true, "writable":true},
{ "name": "Heat Pump Mode bit2", "address": 33, "bus_datatype": "bool", "datatype":"uint16", "type": "register", "value_bitmask":0x4, "write_bitmask": true, "writable":true},
{ "name": "Heat Pump Control", "address": 33, "bus_datatype": "bool", "datatype":"uint16", "type": "register", "value_bitmask":0x100, "write_bitmask": true, "writable":true},
{ "name": "Heat Pump Inverter Mode bit1", "address": 33, "bus_datatype": "bool", "datatype":"uint16", "type": "register", "value_bitmask":0x200, "write_bitmask": true, "writable":true},
{ "name": "Heat Pump Inverter Mode bit2", "address": 33, "bus_datatype": "bool", "datatype":"uint16", "type": "register", "value_bitmask":0x400, "write_bitmask": true, "writable":true},
Posts: 8189
Threads: 43
Joined: Jun 2015
Reputation:
473
It will work but you would still have separate control and status for all bits.
Use this instead. 2-bit values will be mapped to 1-byte objects where you can define custom values for the 0..3 range.
Code:
1 2 3 4 5
{
"name" :
"Heat Pump Mode" ,
"address" :
33 ,
"bus_datatype" :
"uint8" ,
"datatype" :
"uint16" ,
"type" :
"register" ,
"value_bitmask" :
0x6 ,
"write_bitmask" :
true ,
"writable" :
true },
{
"name" :
"Heat Pump Control" ,
"address" :
33 ,
"bus_datatype" :
"bool" ,
"datatype" :
"uint16" ,
"type" :
"register" ,
"value_bitmask" :
0x100 ,
"write_bitmask" :
true ,
"writable" :
true },
{
"name" :
"Heat Pump Inverter Mode" ,
"address" :
33 ,
"bus_datatype" :
"uint8" ,
"datatype" :
"uint16" ,
"type" :
"register" ,
"value_bitmask" :
0x600 ,
"write_bitmask" :
true ,
"writable" :
true },
Posts: 187
Threads: 43
Joined: Jul 2015
Reputation:
2
(21.03.2022, 13:53) admin Wrote: It will work but you would still have separate control and status for all bits.
Use this instead. 2-bit values will be mapped to 1-byte objects where you can define custom values for the 0..3 range.
Code:
1 2 3 4 5
{
"name" :
"Heat Pump Mode" ,
"address" :
33 ,
"bus_datatype" :
"uint8" ,
"datatype" :
"uint16" ,
"type" :
"register" ,
"value_bitmask" :
0x6 ,
"write_bitmask" :
true ,
"writable" :
true },
{
"name" :
"Heat Pump Control" ,
"address" :
33 ,
"bus_datatype" :
"bool" ,
"datatype" :
"uint16" ,
"type" :
"register" ,
"value_bitmask" :
0x100 ,
"write_bitmask" :
true ,
"writable" :
true },
{
"name" :
"Heat Pump Inverter Mode" ,
"address" :
33 ,
"bus_datatype" :
"uint8" ,
"datatype" :
"uint16" ,
"type" :
"register" ,
"value_bitmask" :
0x600 ,
"write_bitmask" :
true ,
"writable" :
true },
Thank you