This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Thermostat
#1
Hi, 

I have several zones of heating/cooling/ducted ac

Obj per zone are 

Room on/off (binary obj)
Room temp 
Room setpoint 
Room output (binary obj)

Global obj,
System mode, heat|cooling (binary obj)

I’m not sure what the best way to do, event script, resident script 
I need to achieve 

If room is off output is off 
If room is on, 

if global mode is heating and temp > setpoint output is on 
else if not then output is off

if global mode is cooling and temp < setpoint then output is on 
else if not then output is off

If temp changes while room is on re eval setpoint and adjust output if required 

Should I do an event script, triggered by tag? 
I looked into the pid script, but that achieves proportional control of the output?
Reply
#2
You can use a resident script for this because you don't need instant reaction to the temperature/mode changes. 2-point thermostat is ok for this task but you should add hysteresis so the output does not bounce between on/off when room temp is near the setpoint. For example, in heating mode the output turns on when room temp < setpoint but turns off when room temp > (setpoint + 1).