This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus RTU and TCP
#3
(06.05.2022, 08:22)admin Wrote: Read delay blocks the whole Modbus mapper operation so no other read or write can happen.
Since RTU1 and TCP are shared one solution is to disable RTU1 and move your device to RTU2. This will solve the TCP blocking issue.
Writing is handled only after a complete polling cycle is finished. Does the same 1 register per second rule apply to writing?

Yes it's the same to write...

Are write requests queued or only last one is done? I mean, if during polling cycle we write 1-2-3 to an address, will the three values be written to the same address or only the last one?