This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Can BUS
#8
You can try swapping GW 2 and 3 and see if it's still not working correctly. If it does not then maybe the hardware is faulty and must be replaced.
As for ballasts this can only be checked with an oscilloscope on the DALI line near the gateway. Then standard says that high level is from 9.5V to 22.5V and low level is below 6.5V. Value between 6.5V and 9.5V is undefined.
Reply


Messages In This Thread
Can BUS - by DGrandes - 20.05.2022, 07:18
RE: Can BUS - by admin - 20.05.2022, 08:18
RE: Can BUS - by CristianAgata - 20.05.2022, 10:00
RE: Can BUS - by davidchispas - 01.06.2022, 13:39
RE: Can BUS - by admin - 02.06.2022, 05:47
RE: Can BUS - by davidchispas - 02.06.2022, 07:51
RE: Can BUS - by davidchispas - 02.06.2022, 10:12
RE: Can BUS - by admin - 02.06.2022, 10:31
RE: Can BUS - by davidchispas - 02.06.2022, 13:03
RE: Can BUS - by admin - 03.06.2022, 06:09
RE: Can BUS - by davidchispas - 03.06.2022, 07:51
RE: Can BUS - by davidchispas - 03.06.2022, 06:20
RE: Can BUS - by admin - 03.06.2022, 10:21
RE: Can BUS - by davidchispas - 08.06.2022, 08:22
RE: Can BUS - by davidchispas - 08.07.2022, 09:38
RE: Can BUS - by admin - 08.07.2022, 09:43

Forum Jump: