This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

CPU Temp
#3
(01.07.2022, 06:06)admin Wrote: CPU max allowed temperature is +95C. From our tests it was not possible to overheat it and cause permanent damage.
Load average is different from CPU load as it also includes I/O operations like reading/writing to the SD card.
Due to periodical refresh of the process list you might not see some event scripts the are increasing the load if they finish quickly enough.

Hello

in my project I don't have many things 10 digital inputs with 10 events and 2 continuous running scripts one for sending sms and one for verifying logical AND / OR operations, and one scheduled at 5 seconds for alarm counting.

Despite this the CPU load is 0.61 and the I / O 0.58
and CPU temperature 83 ° C

What can it be ?