Threads: 2
Hi!
I had som modbus profiles who worked fine on two different ports.
Then i added som datapoints from KNX and connected a new component to one of the ports.
Suddenly all modbus communication is lost. I can`t find any components either with RTU Scan og Read test.
What is wrong?
Is there any posibility to vclear or reset the modbus ports?
Threads: 31
Check wiring, maybe you shorted something.
Threads: 13
But if you short RTU port 1.
Would that also affect RTU port 2?
Here everything is down after working on 1 of 2 ports.
Will LM5 block all modbus RTU if there is a serious enough fault on 1 port?
Threads: 31
Yes
Threads: 13
Thanks for advice. We did all that. And it didn't help.
BUT; we changed borth ports from Full-Duplex to Half-Duplex
And now everything works.
Am not sure if both were Half-duplex before and some-one/thing changed this to Full-duplex..
But it is all running on half atleast..
RS485 is a half duplex connection. Setting full duplex mode will prevent ports from working correctly. For RS485-2 full duplex mode enables RS232 instead of RS485.
Threads: 2
One one of my LM I have a Modbus RS485 issue. I can get out data 1 out of 2 times. One call goes OK and I get data, second call results in a CRC error. I tried this with a readtest under Modbus. When I get a CRC error, the communication LED on the Janitza unit flashes green (that is OK).
With a profile that works on my other LM everything goes right.
I want to read out a Janitza power meter UMG20CM (it has a communication led), this device has Modbus address 1, speed 9600
I tried the following things:
a/ reverse polarity (then always crc errors, red error led on Janitza meter for communications)
b/ connect GND of LM and Janitza: no difference
c/ checked if the fase and neutral of the LM and Janiza aren't switched
d/ tried to lower speed 38400 --> 9600
e/ tried parity al variants (now no, 1 stopbit)
f/ tried other cabling, twisted pair stranded cable
Any tips to try?
Have you tried using a different RS485 port on LM?
Threads: 2
Sorry for the late answer. The problem is that this is on a remote location (>500 km). I didn't try the other port yet.
Any other suggestions?