Bacnet and Number of user for APP Logic Machine
we use logic machine for a lot of integration but we didn't ever integrate a bacnet device.
There are a lot of different limit about maximun bacnet element on the forum suggested but we would ask the limit in our case.
We need to read almost 600 imported element from a bacnet device. We don't need a realtime reading but only a reading every 15 minute and we must log these readings.
The logic machine 5 lite is capable of doing this thing ? Or is better to divide this task on multiple LM ?
In addiction we need to visualize this data. We have 60 different users with unique page. These users need remote access to the device with the cloud (because they don't access to the local network).
It is possible to use the logic machine app for this number of user ?
Thank you.
Bacnet client on LM was created for a small integration, something like 50 objects. The new integration:
https://forum.logicmachine.net/showthrea...1#pid29271
might let you add more but this was not tested on bigger site.
If users will communicate via cloud then the load is on the cloud not LM.
You can read all objects from a single BACnet device: https://forum.logicmachine.net/showthrea...7#pid22457
Depending on king of logging a single LM might not be enough if for example you need to create 600 trend logs.