This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

"Connect" modbus devices
#1
Hey together,

i finally made it and can read values from my modbus devices (thank you Daniel). I thought that if i connect both devices with one object that the value will be written to the other modbus device. In particular i am talking about a PV inverter and a heat pump. I want to send the values of the current DC production and und current DC Export to the heat pump. But somehow it does not work. Unfortunately i didn't find any information in the forum. 
The steps: i read the values of the inverter and write it to an object 12/1/1 and 12/1/2 (write on bus enabled)
I added the heatpump and connected the datafields to 12/1/1 and 12/1/2

Below i send you the Profil for the heatpump.
Code:
{
    "manufacturer": "IDM",
    "description": "Heat Pump",
    "mapping": [
      {
        "name": "Aussentemperatur",
        "bus_datatype": "float32",
        "datatype": "float32",
        "type": "inputregister",
        "address": 1000,
        "units": "°C",
        "value_multiplier":1,
        "writable": true,
        "read_swap": "n"
      },
      {
        "name": "Aktueller PV Überschuss",
        "bus_datatype": "float32",
        "datatype": "float32",
        "type": "register",
        "address": 74,
        "units": "kW",
        "value_multiplier":1,
        "writable": 1,
        "read_swap": "n"
      },
      {
        "name": "Aktuelle PV Produktion",
        "bus_datatype": "float32",
        "datatype": "float32",
        "type": "register",
        "address": 78,
        "units": "kW",
        "value_multiplier":1,
        "writable": 1,
        "read_swap": "n"
      },
      {
        "name": "Aktuelle Leistungsaufnahme",
        "bus_datatype": "float32",
        "datatype": "float32",
        "type": "inputregister",
        "address": 4122,
        "units": "kW",
        "value_multiplier":1,
        "read_swap": "n"
       
      }
     
     
    ]
  }
is the procedure wrong i should have done it with a script? (German manual)
Can somebody help me out with this? i have seen several threads about connection the idm heatpump with iobroker but i didn't see a difference to my parameters.

thx in advance
Reply


Messages In This Thread
"Connect" modbus devices - by Stieges - 05.01.2024, 11:30
RE: "Connect" modbus devices - by Daniel - 05.01.2024, 11:46
RE: "Connect" modbus devices - by admin - 05.01.2024, 11:56
RE: "Connect" modbus devices - by Stieges - 05.01.2024, 12:28
RE: "Connect" modbus devices - by Daniel - 05.01.2024, 12:41
RE: "Connect" modbus devices - by Stieges - 05.01.2024, 14:03
RE: "Connect" modbus devices - by Daniel - 05.01.2024, 14:14
RE: "Connect" modbus devices - by Stieges - 26.01.2024, 15:00